4

Could you please help me answer the following questions?

1) Will unplugging my water heater from the socket when not in use damage it?

2) Which energy-saving timer will work with my water heater?

Below are details of my water heater.

Company: Rheemglas Standard (Energy Miser)

Water Heater Model #: 0199B54937

Wattage: 240/208 Volts AC ONLY

Upper: 4500/3380

Lower: 4500/3380

Total: 4500/3380

Already Tried: I have already tried contacting Rheem customer support; however, no one has responded to my inquiry yet.

Listed UL Water Heater 786H

EDITED

Temporary picture gallery showing (1) electric water heater plug, (2) air conditioner's stand-alone switch, and (3) air conditioner unit above electric water heater.

Pics added inline enter image description here

enter image description here

Harper - Reinstate Monica
  • 313,471
  • 28
  • 298
  • 772
TechEnthusiast
  • 51
  • 1
  • 1
  • 6

2 Answers2

6

I would suggest a timer like this. Additional start/stop pins can be added if you decide on adding a second on off time (or more) and you can always flip the over ride to the On position. This way your water will be hot in the morning instead of having to wait after you turn it back on.

The only problem is if there is a power outage you would need to adjust the clock face (very easy). I would suggest an absolute minimum rating of 30 amps. This model is rated at 40 and I have had excellent long term service with this brand and style.

isherwood
  • 158,133
  • 9
  • 190
  • 463
Ed Beal
  • 103,727
  • 4
  • 79
  • 158
3

Do not plug and unplug that outlet on a daily basis. That is probably a 30A rated receptacle (probably NEMA 6-30 or 14-30) and those are not rated for frequent use. (Most especially the obsolete NEMA 10-30 -- it would be illegal except for the rationale that it is rarely unplugged and is therefore unlikely to fail deadly.)

I'm unclear on what the box is, in your second photo. I don't see an operating handle but it's the right size to be an ultra-heavy grade switch. If it controls only the water heater, you can use that to turn it on/off.

A timer would be fine. We're not a shop-for-you site so I don't recommend any particular product.

In our similar installation, we added a plain switch. (heavy-duty of course). I have my eye on a "twist" timer switch like you see on bathroom heat lamps. They can be had in times 0-5 minutes clear up to 0-12 hours -- and with or without an "always on" detent.

enter image description here

You could even use a "smart switch" and command the heater to turn on with your phone.

Or the cheap option is to change the circuit breaker to one that is listed for daily use as a switch. Some breakers are.

Anything you use must be rated for the amperage of the receptacle, wire and breaker, for instance you are not allowed to use 20A-rated gear on a 30A receptacle. Also the device must be UL-listed (or whatever your region's listing authority is) - and it must have a proper enclosure, no dangling devices or exposed terminals. And be properly mounted.

You may run into a problem where you love a switch/timer, but it cannot support 30 amps. Don't use it directly: use a relay do the heavy switching. This is getting a little more complicated, but not terribly so. The relay must be rated for 30A, but the devices controlling the relay do not.