3

I am finishing up installing my generator transfer switch today and I think I have a wiring problem...

I have a six circuit transfer switch wired in with a power inlet box outside. Everything is wired in and I am doing the final check before hooking up the generator. For checking the wiring, I am doing a continuity check between all four conductors. When the transfer switches are all in the "Line" position, I have continuity between neutral-ground and none in the other five combinations (L1-L2, L1-N, L2-N, L1-G, L2-G). With the transfer switches set in the "Off" position, I have the same continuity readings.

The problem (I think) is that when I put the transfer switches in the "Gen" position, I have continuity between every conductor!

I am 99.9999999999% certain this ain't right. Any ideas on where to look first? I am headed back to the basement to open the panel again and double check all the obvious things.

Aarthi
  • 1,143
  • 7
  • 20
  • 29
Dave Nay
  • 1,664
  • 1
  • 14
  • 15

1 Answers1

2

If you are testing continuity at the generator inlet plug with the transfer switch in the GEN. position, you will be measuring continuity throughout the entire circuit. If you look at this image, you should see why you're getting the readings you are.

enter image description here

The light blue box on the left, represents the main service panel. The light blue box on the right, represents the transfer switch.

Have the installation inspected by a certified licensed electrician before using the generator, to make sure the transfer switch is installed properly. Remember, peoples lives could be on the line here (pun intended). Back feeding caused by improper transfer installation, can kill linesmen trying to restore electrical service to your home during an outage.