Details: 240/120V split phase
Using my clamp on amp meter the readings on leg A was 3.2. on leg B 2.6 ( a .6 difference ). The neutral read 1.9 ( a 1.3 difference ).
Is the 1.3 Amps something to be alarmed about? If not, what would be considered reasonably alarming?
Kris
  • 4,865
With Measurements made on loads that have nonlinear characteristics the totals don't always add up the way you would expect. Variable speed motor drives, dimmer circuits, modern flouresent ballast are all devices that can cause interesting voltages and diferent amp draws on each leg. I thought I would also add on a 20 amp electronic furnace I recently worked on when running at low speed had over 9 amp imbalance but at full speed the the imbalance was less than 1 amp. For this reason the NEC considers the neutral to be a current carying conductor with nonlinear loads.
Ed Beal
  • 103,727
  • 79