I have an unused 240V, 3 prong (2-conductor) dryer outlet in my garage and would like to convert that into two 120V supplies to some overhead lights and a ceiling outlet for a garage door opener. How do I split that 30A 240V supply into a couple of different 120V 15A circuits? I don't expect any more than a couple hundred watts of intermittent load per circuit.
nobody
  • 7,701
  • 47
Knob Scratcher
  • 421
Depends how much work you want to do. The simplest approach given: " I don't expect any more than a couple hundred watts of intermittent load per circuit."
Is to convert it to a single 120V circuit at 20 amps, 2400W capacity; (or 15A, depending what the total expected wattage actually is) that happens to have vastly oversized wires. Replace the dual-pole 30A breaker with a single pole 20A breaker, use one of the hots (retagged green) to ground, [or retagged white to neutral if the current "neutral" wire is already at the main panel ground/neutral buss and it's more convenient to make THAT one the "green/ground" wire] change the receptacle, perhaps add a few boxes connected with at least 12Ga copper to house some additional outlets, away you go.
Now, if it's easy to run a ground wire, (or by some miracle the cable actually has one already, unused) you can do that and convert to a 4-prong, and then my answer in the "near duplicate" linked above applies. Several other options were provided that ignored that poster's desire not to do anything in the panel - if you are OK doing things in the panel, they also apply if you like them better. You could replace the receptacle with a sub-panel, for instance.