I'm rewiring outlets and switches in our 1960's California home using AlumiConn connectors to connect the aluminum wiring to copper pigtails. Most cases are straightforward, but I've run into a case where a box (a double-sized box, thankfully) includes a joint of the neutrals of 4 aluminum wires (10 gauge each). AlumiConn's only come with a max of 3 ports.
What is the correct way to handle 4-wire connections? Is it correct to daisy chain the AlumiConns?
Lacking any other instructions, my instinct would be to wire them like this, but I don't know if this is acceptable, safe or correct:
  AL  AL      CU      AL     AL
,--._,--._,--.   ,--._,--._,--.
|  AlumiConn |   |  AlumiConn |
mhucka
  • 285
You have two options here
You have two options here. Either you can daisy-chain AlumiConns as you describe, using 12AWG copper THHN for the jumper wire, or you can use a single Al/Cu rated mechanical tap connector (often called "Polaris connector") rated for the wire sizes in question (the smallest size you'll find can take anywhere from 14 to 4 AWG), provided the latter will fit into the box. An ILSCO PBTS-4-4, for instance, takes up about 2" by 1.3" by 1.4" (LxWxH) and requires a torque setting of 20 in-lbs for 14-10AWG wire. Either way, you'll need to torque these connections correctly, as you are already doing with your existing AlumiConns.
Or well, three now
While they weren't a thing at the time this answer was originally written, Ilsco has introduced their MAC-Block connectors, which'd accommodate a 4-port setup like yours (2 wires in each of the 2 ports) more compactly than either of the two approaches above. Their availability in retail channels may still be spotty, though; your best bet is to try an electrical supply house that stocks Ilsco products.
ThreePhaseEel
  • 87,685
  • 144
  • 243