I recently got a circuit added to my spare room to grow some tomatos, the lighting I am going to be using is 8amp on each plug, I noticed the electrician didnt install a 20A rated receptacle with the side blade but installed a 15amp instead. I am wondering if this is safe, it is the only receptacle on the line. Pretty simple fix to swap it out if need be enter image description here

isherwood
  • 158,133
  • 9
  • 190
  • 463

2 Answers2

2

That is fine. If there was only a single receptacle then it would have to match the 20A circuit. With a duplex, 15A is fine on 20A circuit. It matches your usage perfectly as each receptacle will use less than 15a and together more than 15 but less than 20.

manassehkatz-Moving 2 Codidact
  • 139,495
  • 14
  • 149
  • 386
0

Yes, that is fine.

Normally, the rule is that the socket size must match the breaker size. However there are two exceptions:

  • 15A receptacles are allowed on 20A circuits, as long as there are at least 2 sockets on the circuit. This is supported by a UL rule that requires the internal wiring of all 15A sockets certify for 20A passthru.
  • 50A receptacles are allowed on 40A circuits because nobody makes a 40A receptacle.