After my own inspection and talking to the utility company I have the following:
  • The meter (near the road) is 5/8" x 3/4". From what the water company told me - this is the most commonly installed size service in this area.
  • There is approximately 180ft of 3/4" PVC and 3/4" PEX coming off the meter to my house where it connects to a 3/4" copper trunk line. (The first 100ft or so is PVC and the rest is PEX that I installed recently to replace a section of galvanized, corroded pipe.)
  • My hose bibs which are fed from 1/2" branch lines (and before a PRV) measure approximately 5.2 GPM @ 70 PSI (tested with a flow gauge and pressure gauge at the bib w/ no other fixtures in the house being on)
My questions are:
  • Does 5.2 GPM seem pretty low? It seems barely adequate to get spray things clean at times. It barely seems able to feed my pressure washer at times.
  • Would changing that 180ft main line with 1" improve anything?
I've inquired with the utility about the cost of changing my meter to 1" as well. That would be pretty costly but not crazy (around $2k).
Thanks in advance for any guidance.
Freddie
  • 101
I would assume there's a pressure regulator somewhere after the meter mounted on your house ?
Loosening the locknut(s) and turning the adjustment clockwise will increase that flow.. You might not have to go thru all this, if your place has a pressure regulator.
Increasing the supply pipe size will allow a higher flow rate due to reduced resistance. If you replace the water meter with the next size, you will have to absorb the cost, and there is usually a higher monthly cost for that meter. I never measured the flow rate in my house but I would have to assume that 5.2 GPM @70 psig should be adequate for most high flow devices like a hose or pressure washer. Another problem that may effect the flow would be the piping inside your home.
d.george
  • 12,593