I have a 240VAC garage outlet that will be turned on via a control relay. Is it best practice to switch/relay both lines, or just one like 120V~ loads?
I'm assuming your wanting to power some 240V appliance with this circuit. In that case, if you switch off only one of the two HOT wires, you will likely cause a problem with the appliance, depending on what it is.
Yes, you would definitely want to use a double-pole 240V rated relay for this application.
- 23,628
- 2
- 34
- 65
Legally, it is acceptable to switch only one pole of a 2 pole circuit, as it will not allow a 240V device to operate. If you think about it, that is what happens with fuses, they RARELY both clear at the same time.
But that does not apply to circuit breakers, which are required to operate both poles at the same time.
Still, just because you can does not mean you should. If switching a 2 pole circuit, it's best to use a 2 pole contactor. ("Relay" generally means small control type circuits, for power, you call it a "contactor").
When selecting a contactor, you need to assess the nature of the load you will be switching. if it has a motor, the motor HP ratings will not align with the current ratings, because switching of inductive loads like motors is harder on the contacts than switching simpler things like resistors or lamps. So for example if you have a 1HP motor rated at 8A @230V single phase, you would think that a 15A relay would suffice, but most 15A relays are only rated for 1/2HP. Read the fine print.
- 15,146
- 1
- 20
- 40