Almost all of the radiators (forced water) in my house heat up fine. However, a single radiator needs regular bleeding (~1/day) in order to heat. Note, this radiator is not at the highest point in the house (it's a split level; I'd say it's around 3/4 of the way up), and radiators higher up are plenty hot.

Also, there no obvious water/corrosion stains around this radiator.

What might be causing this problem, and how do I fix it?

Eli Lansey
  • 251
  • 1
  • 3
  • 9

2 Answers2

2

When you do your daily bleed of this radiator if you don't actually get air coming out, just water. You don't have an air problem, you have a water flow problem.

If your system a diverter-tee system (a "one-pipe" system), check to make sure that the tees that feed this radiator are installed the same way as the tees that feed your working radiators. The diverter tee for this radiator should be on the return side, and the stripe (or other indicator of orientation) should be between the branches. An incorrectly installed tee could cause the exact problem you're describing.

Tester101
  • 133,087
  • 80
  • 327
  • 617
Brian R.
  • 29
  • 2
1

I can't say for sure what might be causing it but if when you bleed it you do get air coming out a simple fix may be to install an automatic bleeder. These are screw in replacements that go where the existing bleeder screw is. You adjust it so that it is just tight enough to not let water out, and the idea is it will automatically release small amounts of air. How well these work is debatable, but it might be a $6 fix to your problem. I grabbed a few of these : http://www.homedepot.com/p/Plumbers-Edge-Automatic-Air-Valve-PE970/300011259