When wiring 15A-rated outlet receptacles on a 20A circuit, is it acceptable to use the tabs & screws to chain the circuit from one outlet to the next?
My instinct to overengineer says to use pigtails to pass the power to the next outlet and wire the receptacle, but this takes up more space in the box. So is the tab on a 15A outlet sufficient for handling a 20A load though a series of outlets? if so, why?
jamietre
  • 213
Yes it is sufficient.
A 15A receptacle is designed such that an appliance with a 20A plug should not be able to plug into it. This means that at most under normal operating conditions of a 15A appliance, that the receptacle itself will only draw 15A. If the circuit shorts then the breaker will kick at 20A however.
The tab of a 15A receptacle is designed to handle a 20A load.
EDIT for clarification above: A duplex 15A receptacle contains a tab that connects the hot lead to the hot load. This allows the receptacle to carry the load of another outlet by wiring the lead of Outlet(2) to the load of Receptacle(1). When you break off this hot tab then you are specifically wiring for a switch to control only of the receptacles of the outlet, or you are specifically wiring for each receptacle to have its own circuit on a shared neutral. For two circuits to be wired to a single receptacle on a shared neutral, then you need to ensure that the breakers are on different service legs or you risk overloading the neutral. If you also break the neutral tab then you are wiring the receptacle to have two separate circuits each with its own dedicated neutral. These should be considered fringe cases for residential so it is probably best not to break the tabs if not needed so as to avoid confusing future DIY'ers and licensed electricians. Every time a DIY'er or electrician gets confused then they are potentially risking themselves.
The NEC states that this is acceptable as long as:
  1. The wire is 12 AWG sized for a 20A circuit
  2. There is more than one receptacle on the circuit.
It is important to note that under no circumstances should you install a single 15A receptacle onto a dedicated 20A circuit. This is against code.
210.21(B) Receptacles (1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
(3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or where larger than 50 amperes, the receptacle rating shall not be less than the branch-circuit rating.
Table:
Circuit Rating (Amperes)
Receptacle Rating
(Amperes)
15 Not over 15
20 15 or 20
30 30
40 40 or 50
50 50
In conclusion, a standard 15A receptacle that one would buy in your hardware store is quality tested and approved to comply with all NEC codes to be legally sold in the United States. If the tab couldn't handle a 20A load without overheating then they would call this out specifically.
maple_shaft
  • 3,231
  • 35
  • 49
NEC 2011
210.19 (A)(2) Branch Circuits with More than One Receptacle. Conductors of branch circuits supplying more than one receptacle for cord
and plug connected portable loads shall have an ampacity of not less than the rating of the branch circuit.
This tells me that the circuit should be pig tailed so the receptacle does not carry the load of the rest of the circuit. Also: if you have been testing arc-fault circuits with an arc fault tester the circuit may not trip due to the voltage drop, high impedance or low resistance, but with pigtails the resistance is increased and the impedance is lowered allowing for proper arc-fault operation.
You shouldn't use 15A outlets on a 20A circuit. The 15A outlets are only rated for 15A. There is the risk for overheating and potential fire at the 15A circuit location before the 20A breaker would pop.
I always like to use pigtails and the inspector in my area agrees. It's never happened to me, but if an outlet fails and you don't use pigtails, the rest of the outlets downstream could be affected.
bdowden
  • 135