6

I've seen discussions of using an old 240V wire (two hots, a neutral, and a ground) and reconfiguring it to have two 120V circuits.

As an example, if it is a 20A cable, you could have two 20A circuits, each one using one of the two phases and both sharing the neutral and ground.

If each circuit is powering a device using the full 20A, would this result in 40A of current going onto the neutral, causing overheating?

Additionally, will sharing the neutral cause interference between the circuits?

brentonstrine
  • 1,080
  • 6
  • 21
  • 37

2 Answers2

7

Actually, it would result in a net 0 A on the neutral. So this actually can work quite well and is called a Multiwire Branch Circuit or MWBC.

The one catch is that the breakers powering the circuit need to be set up for common shutoff - i.e., if you turn off one, you always turn off the other. If the breakers are actually set up for common trip, which is normally the case for a 240V circuit like a stove or dryer, then that provides common shutoff as well.

manassehkatz-Moving 2 Codidact
  • 139,495
  • 14
  • 149
  • 386
6

Just to expand the explanation in the answer from @manassehkatz:

On a USA-type 240 volt circuit, you actually have two 120 volt hots, as you know, but the AC signal is 180 degrees out of phase. So when one hot is at +170 volts (peak voltage for 120 volts RMS), the other hot is at -170 volts and when one hot is at 0 volts, the other hot is also at zero.

The result is that on a 20 amp circuit, the most current that can travel over the neutral is 20 amps and this occurs when the load is completely unbalanced: 20 amps on one hot and 0 amps on the other. In this case, all of the current from the load returns over the neutral.

On the other extreme, if both hots have a 20 amp load, then all of the current from one leg returns over the other (effectively, the two loads are in series) and no current has to travel over the neutral.