I'm living in an old apartment, and my roommate has fed electrical cords through a heating vent from the living room into the bathroom, up to a power bar on the side of the sink. I see this as a double hazard and illegal.

The heating vent exits from the wall behind the toilet, about 3 inches off floor. He says it is safe because the power bar and the cords behind the toilet will not cause a fire because the heat in the vent will dry any condensation that might cause an electric fire. But wouldn't using an active vent be dangerous, as well as being near water?

I know very little about any of this, but doubt any amount of safety or grounding will make this safe. Would anyone know how to make this situation safer? Or give me some peace of mind so I can sleep.

Update:

This roommate is a contractor and is educated through college for home renovations. I cannot convince him to remove this hazard and will move out soon. I was told I was overreacting and do not understand how it works...so I appreciate the confirmation that it is dumb and dangerous.

Darrick Herwehe
  • 379
  • 1
  • 11
Felicia
  • 161
  • 1
  • 1
  • 4

5 Answers5

20

Any electrical socket in a bathroom must have GFCI protection. You're damp, you touch something with a ground fault, feel a slight tickle and wake up wearing a halo and wings. Of all places to hack together power supplies, a bathroom is absolutely the worst place to do this. Mystical theories about the heater protecting the strip from dampness don't remove the shock hazard.

Fire hazard is not your problem here

Fiasco Labs
  • 11,431
  • 1
  • 29
  • 44
16

I don't know your location, but in the USA, it is strictly forbidden to run any electrical wiring through heating vents or any air handling plenum. The reason for this is that you now have a combustible material in the plenum, that can spread a fire between rooms and into wall cavities. As previously mentioned, any AC electrical outlets in a bathroom MUST be GFIC protected. If you do not have electrical outlets with GFI protection in your bathroom, take it up with your landlord and ask that a safe source of electricity be installed. Meanwhile, get that extension cord/plug strip out of there.

shirlock homes
  • 58,628
  • 3
  • 87
  • 168
3

It's not safe and not good practice to run anything through heat vents. Why can't he use the electricity in the bathroom?

Sam
  • 121
  • 1
3

You can reduce the risk of electric shock due to a ground fault (e.g. caused by moisture) using one of these GFCI plugs. Since it sounds like the extension cord starts in the living room, you would use it at the outlet there. It will protect anything downstream the same way a GFCI outlet would. However, this is not a fantastic solution and doesn't solve the issue of the HVAC vent.

Obviously the best solution is to remove the power strip and/or find another place to live.

Hank
  • 14,213
  • 10
  • 46
  • 48
2

Your roommate is an idiot who needs to be soundly bludgeoned over the head with a paper copy of the NEC until he gets electrical safety drilled into his thick skull.

Tell him that the county electrical inspector will ask him if he's wearing a halo and wings already until he corrects the violations of 210.8(A):

(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuit-interrupter protection for personnel.

(1) Bathrooms

300.22(B):

(B) Ducts Specifically Fabricated for Environmental Air. Equipment, devices, and the wiring methods specified in this section shall be permitted within such ducts only if necessary for the direct action upon, or sensing of, the contained air. Where equipment or devices are installed and illumination is necessary to facilitate maintenance and repair, enclosed gasketed-type luminaires shall be permitted.

Only wiring methods consisting of Type MI cable without an overall nonmetallic covering, Type MC cable employing a smooth or corrugated impervious metal sheath without an overall nonmetallic covering, electrical metallic tubing, flexible metallic tubing, intermediate metal conduit, or rigid metal conduit without an overall nonmetallic covering shall be installed in ducts specifically fabricated to transport environmental air. Flexible metal conduit shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable equipment and devices permitted to be in these fabricated ducts. The connectors used with flexible metal conduit shall effectively close any openings in the connection.

and, of course, 400.8:

400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:

(1) As a substitute for the fixed wiring of a structure

(2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors

ThreePhaseEel