I've 2-runs of 12/2 w/G romex supported to studs from breaker box up to where it needs to run unsupported 20' through and alongside (parallel) floor joists of finished floor/basement ceiling for 20' to a junction box at other end where again it'll be firmly supported to studs. My QUESTION is it OK to have it laying unsupported on the sheetrock ceiling while only being fastened to studs on both ends. Basement ceiling is finished I prefer not chopping into it??
Asked
Active
Viewed 327 times
This is fine
What you are describing falls under NEC 334.30(B) point 1:
(B) Unsupported Cables. Nonmetallic-sheathed cable shall be permitted to be unsupported where the cable:
(1) Is fished between access points through concealed spaces in finished buildings or structures and supporting is impracticable.
So, go ahead and fish the cable through the ceiling as you plan to do.