According to the Black & Decker Wiring book, the NEC indicates that each room should include at least one "switch-operated lighting outlet". Is that true even in rooms that have overhead lighting, or does that count as the "outlet"?

JACK
  • 89,902
  • 21
  • 80
  • 214
Trevor
  • 785
  • 1
  • 8
  • 15

3 Answers3

51

TLDR: an overhead light is a fine "outlet" here.

I think the issue is NEC definition of outlet vs receptacle

Outlet. A point on the wiring system at which current is taken to supply utilization equipment.

Receptacle. A contact device installed at the outlet for the connection of an attachment plug, or for the direct connection of electrical utilization equipment designed to mate with the corresponding contact device. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.

The NEC requirement for lighting is:

210.70(A)(1) Habitable Rooms. At least one wall switch–controlled lighting outlet shall be installed in every habitable room, kitchen, and bathroom.

You need an outlet, which can be a hard wired fixture, or could but not necessarily be a receptacle.

(Quotes 2017 NEC)

Harper - Reinstate Monica
  • 313,471
  • 28
  • 298
  • 772
NoSparksPlease
  • 20,598
  • 2
  • 21
  • 51
10

A "lighting outlet" in NEC terms (or possibly black&decker rewording, or old NEC language that may have been updated since that book) includes an overhead light.

Ecnerwal
  • 235,314
  • 11
  • 293
  • 637
6

Each entrance to a room needs a switch that can operate a light. It can be by an wired overhead junction box in the ceiling or a switched duplex outlet.