2

I'm hoping to replace my thermostat with an Arduino-powered one of my own. The furnace is a Trane XV90 Upflow 2-stage condensing gas-fired one with upgraded inducer motor using Trane Furnace Kit KIT15017. No cooling.

I'm following this guide to understanding thermostat wiring, which recommends:

Measure the voltage between the terminal C and the rest of the terminals. Set your thermostat on the different modes (AC, HEAT…) and check what terminals are energized on each function.

This will give you a pretty good idea of the terminals that you will have to connect to activate the different modes.

But I don't have a C terminal. Here's what I have: enter image description here

So I have two issues:

  • No exposed C wire for measuring with multimeter
  • Accessing the terminals requires removing the thermostat. Won't this turn off my heat, and I won't be able to measure any activity anyway?

EDIT

So here's the wiring at the furnace: enter image description here

Sanity check passes that the colors/labels align on this end, but it bothers me it doesn't match the wiring diagram from the manual:

enter image description here

For the silver lining, I spy that this end labels "B" as "B/C." Am I on to something?

Second edit: As for how to measure with a multimeter during operation, I postulate I could probe these furnace-side terminals instead of thermostat-side terminals. The system senses the furnace burner door being opened (required to access terminals) with a simple switch, foolable with an inch of duct tape. Now I can probe while the thermostat is plugged in, giving commands, and outputting system status.

Can I get a sanity check that my logic is correct before I proceed? Once I proceed, I can quickly solve the prior issue (whether 'B' is my common, I guess?) by sensing voltage difference between it and the 'R' wire.

armani
  • 123
  • 1
  • 5

1 Answers1

1

B is your C

Your thermostat base uses B to denote what other folks denote as a C wire; we can confirm this by looking at how it's wired to the B/C terminal on your control board via the blue wire in your thermostat cable.

And your approach to testing is sound

Your approach to testing the thermostat connections at the furnace-side with the interlock defeated is generally how it is done, yes. Do be careful to remember to remove the duct tape flag before returning the furnace to service, though!