Working in a 1960's house and trying to go through and see what breakers go to what, so I can write everything down, just to have knowledge.

I have one 20 amp circuit (for kitchen and dining room) with a 12/2 wire going first to a single 15 amp small round floor outlet (not a duplex), then it goes to two 20 amp duplex wall outlets, then over and up to two 20 amp kitchen wall outlets and finally a 15 amp outlet on dining room wall. Will this work OK, with the first outlet being a single 15 amp, since I read you can't have a single 15 amp outlet on 20 amp circuit, or does that mean you just can't have a 15 amp outlet without other outlets on that circuit?

Machavity
  • 26,498
  • 8
  • 44
  • 100

2 Answers2

12

It means that on a 20A circuit, if the only outlets are 15A, then there must be more than one of them. You're fine with respect to that rule. This means:

  • 1 - 15A - no good
  • 2 - 15A - duplex or two singles - OK
  • 1 - 20A - OK
  • 1 - 15A plus 1 - 20A - OK

And any higher number (15A and/or 20A) is OK.

There are two fairly common modern code compliant situations where a single 15A receptacle will be used as part of a 20A kitchen circuit:

  • Clock - A single receptacle placed on the wall, often recessed, for a clock. Not as common these days as (a) even those of us who never wore a watch commonly walk around with a portable computer that happens to include a clock function, (b) most conventional ovens/stoves and microwave ovens have clocks and (c) many people have a clock radio (or other audio/visual device that includes a clock) in their kitchen.
  • Gas Cooktop - You can install a receptacle for the ignition circuit of a gas cooktop below the cooktop but as part of one of the countertop receptacle circuits.

There are two other things to consider in your situation:

  • GFCI - If you do not already have GFCI protection for the kitchen receptacles, that is highly recommended. You can do that at the breaker - protects everything, whether you like it or not, at the first kitchen receptacle with load wired correctly protecting everything following it in the circuit, or at each kitchen receptacle with load wired correctly (in this case, wires pigtailed to line instead of load) to protect only the kitchen receptacles. This is an important safety upgrade that is worthwhile in every kitchen.

  • Current code limits what places the kitchen receptacle circuits can serve. You may or may not be in violation of that rule, as it is complicated and, I believe, includes at least some non-kitchen locations. You are grandfathered in on this rule, but if you add any new kitchen receptacle circuits (often a very useful upgrade), they should be dedicated to the kitchen.

manassehkatz-Moving 2 Codidact
  • 139,495
  • 14
  • 149
  • 386
3

What trips most people up here is this: how many receptacles does this device count as?

NEMA 5-15R duplex

That's a NEMA 5-15R duplex receptacle (which is ubiquitous in the US). It's a 15A plug but it has two receptacles. It is also rated for 20A pass-through (meaning you can use it inside a 20A circuit). When they mean one receptacle, they mean these uncommon receptacles

NEMA 5-15R single

You can't put this one on a 20A circuit by itself. The reason is that the receptacle would not be properly protected by a device pulling more than 15A. A single duplex receptacle is perfectly fine because you can plug multiple devices up.