I'm looking to connect an electric pottery kiln to an existing subpanel that is serviced by a 10/4 copper line and want to understand if the wire can acceptably tolerate the load.
The wire (installed by previous owner) has the following markings
- "CSA Type ST"
- "105 degrees C"
When in operation the kiln is rated by the manufacturer to draw a steady-state 27 amps (240 V), and that it should be wired on a 35 amp breaker circuit.
Checking my handy ampacity chart notes that #10 can do 30 amp @ 60 C, 35 @ 75 C and 40 @ 90 C. Does the 105 C on the wire mean that I can in theory go beyond 40 amps and still be within safe operating limits? What does it actually mean for a wire to be running at 75 C, 90 C? So long as it's behind walls / in conduits / you're not grabbing it with your hands, does that elevated temp pose any risk?
(I'd have put an #8 wire to this panel if I were installing new, but this line is buried going to a outside workshop so trying to avoid digging that up if at all possible)
Thank you!