I'm moving my dryer from one side of the laundry room to the other one, and extending my circuit from the existing outlet box -- the new length of the run (old+new) is roughly 25 feet.
During an on-site consultation, my licensed electrician suggested I use 10/3 Romex** for this, which also happened to match the recommendation of the staff at the hardware store, where I purchased a spool of 20feet of that 10awg cable. I fished that thing through.
I was sifting through my LG dryer's user manual to figure out a detail, and stumbled on this:
If the branch circuit to dryer is 15 ft. (4.5m) or less in length, use UL listed No.-10 AWG wire (copper wire only), or as required by local codes. If over 15 ft (4.5 m), use UL-listed No.-8 AWG wire (copper wire only), or as required by local codes. [elided]
15ft max on 10/3, why so short?
What possibly could be going on here? I looked at the voltage drop table, and it's something like 1.9V at 25' (30Amp circuit, single phase ~240V AC). Is the manufacturer being paranoid, is my electrician being lenient, what?
Here's the output of the [voltage drop calculator] (https://www.cerrowire.com/products/resources/tables-calculators/voltage-drop-calculator/) for this (I think I'm using it with the correct values):
Regarding my local code (I'm in BC, Canada), it does provide equations that can let me pick the right conductor for the job, but I can't use them without the parameters and tolerances of the equipment attached to the circuit -- which LG doesn't give.
Example:

Click here for full size. (there's a second page of steps to arrive at the answer, which I've omitted)
The specs of the dryer don't reveal much, in terms of max draw, or average power consumption. It just says it needs a 30A circuit, and single phase 230VAC 60Hz, fused at 30A (on both sides of the line).
** 10/3 Romex is a non-metallic sheathed cable with 3 insulated copper conductors (10AWG), and a bare copper. The outlets in my particular case have 4 pins. The dwelling was built in 1990.
Related Questions:
What gauge wire do I need for my dryer? - useful, but answers don't consider the manufacturer recommendations
Dryer connection changes from 10-3 with ground to 10-3 without ground -- long runs of 10/3 seem to be par for the course, anecdotally