I'm running three 8awg THHN thru 1/2" sch-40 to garage, attaching same to existing 10awg NM-B at a J-box TBD in basement ceiling. I may change 10 to 6awg in future. So my questions are ..
  1. metal or plastic j'box, how to join wires internally.. alt for wire nuts ? Something like this but this is aluminum .. is there a copper version that's similar?
  2. read that THHN wire is NOT suitable for "wet" locations. My conduit will be inside wall until inside garage, is this considered wet? Also wire markings indicate this is also THWN so assume this is a non-issue .. please comment and/or confirm.
Thanks, Ron
Ron C
  • 79
As already answered, check the labels but your wire is probably fine.
Metal vs. plastic? Almost always metal is better.
10 AWG to 6 AWG or 8 AWG? Ideal makes wire nuts that will work - e.g., WT54 Blue or 66 Gray/Dark Blue or B4 Blue/Gray.
  • 139,495
  • 149
  • 386
Virtually all modern THHN is also marked as THWN or THWN-2, and possibly also MTW or other grades. So long as one of the several grades is wet, it would be fine if it needed to go outside, but for a connection to an attached garage, not run on the outside of the building, the conduit is a dry location anyway.