I am in the process of planning to upgrade my house's wiring. My house was built in the 1920s. It most likely uses tube and knob wiring. I am not sure as I have not looked in the walls yet. It does use it in the attic. The house currently uses a 100 amp service. The house is 2000 square feet. I am planning to add a 2nd building to the property that would be equal to a 1 bedroom house. I will have each room be on its own breaker. All the work will be done by an licensed electrician.

Here are the steps I am planning to take.

  1. Using a stud finder, I go around marking the paths the electrical wires take through the ceilings and walls.
  2. Map all the outlets and fixtures in the house to specific breakers.
  3. Upgrade the service to 300 amps from 100 amps. This will also replace the current main breaker. I will also add an external main shut off panel near the main meter.
  4. Have the first floor and basement rewired.
  5. Have a subpanel installed on 2nd floor and upgrade wiring on 2nd floor and attic.
Machavity
  • 26,498
  • 8
  • 44
  • 100

2 Answers2

11
  1. How will a stud finder find the wires? Usually, there is no bonafide way to identify a buried wire's run except by trial and error. This is why after virtually every knob-and-tube removal, there are huge patches of wall removed all around the house that need to be plastered, repainted or what have you. If you want to save money, you can get your own oscillating saw and cut out the sections for the electrician so all they have to do is pull wire - otherwise the electrician does the same and still charges you for the time. Lucky owners who had wire run after initial construction have wires that aren't held by staples and can tie a fishtape to the wire and just yank the wire through the wall a considerable distance.

  2. You can do this part by switching the breakers rather than chasing the wire back to the source, hopefully your panel is actually labeled correctly so this isn't technically necessary. You (or electrician) can just transfer breakers and labels to the new panel. If they're wrong for any reason, it's never too soon to correct the labels as needed.

  3. 300 amps is too much - what kind of appliances are you running? And is the second property going to be metered or are you running a subpanel to that property (like a MIL)? Even if both have a electric dryer and range, you can have 100 amp subpanel in the second building and 200 amp main in the main building.

  4. Yes, do the needful.

  5. This seems totally unnecessary. Even if you run a subpanel upstairs, you will have to fish like a 3 ought wire two floors up for just like 20amps tops. Since you're already cutting a dozen holes that will need plaster and paint, why not cut a dozen more to run to the top floor? You still need to get rid of your top floor knob and tube anyway.

AdamO
  • 1,185
  • 1
  • 11
  • 22
9

I just did my own house and...

  • your knob and tube are kinked in insulators inside your walls and are run separate through the home
  • you have lathe behind your plaster. you are in for a real treat
  • you need to replace your drop service (from the main power line),weatherhead, meter socket, panel, and ground everything first
  • you will trace nothing with any non contact tester, you will be cutting holes or gutting it
  • check if you have galvanized pipes. You want to replace those trust me. They are FULL of rust on the inside. That will give you some openings to run wire upstairs. Then wire the 2nd floor from the attic. Outside walls are going to be tough but your house is balloon framed so you basically have a chimney between each stud that goes from the basement to your attic. Should put some fire blocking in there. Look it up, it will save your life.
  • your breakers are not on rooms. you will have west wall living room, north wall kitchen and dining room light. The wires will be soldered together in places, you will see in the attic floor.
  • You cant combine new and old wire first of all. Doing the downstairs you will loose power to upstairs the way the wire was ran back then. Your hallway light on the steps will not work because it's a 3 way and you have one 3-way up and one downstairs.
  • You have no grounds if you have knob and tube as well as metal boxes (crazy right) The number one thing to be weary of is you can not lose a neutral or your house will most likely burn down. Your insurance wont even cover knob & tube as in they will not insure your home at all unless your removing it.
  • adding shut off panel near the main meter...that becomes your main disconnect and everything after is a sub
  • You need to call a licensed contractor and don't worry about your stud finder gadget and messing with any wires. Your panel switching plan needs to be revamped because if your grounds. It makes more sense to drop your SE cable to a main service panel in basement for multiple reasons. You have to have floating grounds to your subs, the wire to run to a sub upstairs...idk my friend. Your 300 amp is not going to happen, what the heck are you running a machine shop? (joking) I want you to be safe. They will do all of that for you, cut the smallest holes so the plaster keys don't break and pop off the wood lathe. It is a big job and your safety and family or friends safety is important. If you do have romex from the 60's it can have asbestos in it, there is tile with asbestos and pipes that may be wrapped in it. I wish you the best of luck and you will see what I am talking about.

p.s. Check your bathroom stack. Now would be the time to get that cast out of there. It probably runs down your staircase wall from the second floor to the basement. It's not if but when that begins to leak because its rusted you will have a mess in those walls. If it is pvc you are blessed. Love my old home (1913) with the oak trim and doors. These houses lived over 100 yrs and after upgrading and insulating, a 100 more.

Have fun and stay safe!