4

I've been having some minor trouble with my ac. When it gets hotter, towards the afternoon, it will lose ground and only be able to cool two degrees higher than what the ac is set to. For example, if it is set to 76, the thermostat will read 78. While it's not unbearable or super uncomfortable, it is a little bit noticeable. It didn't have any trouble the day before maintaining the set temperature, but today it was higher, despite the outside temperature being about the same.

I have changed my filter, put new batteries in the thermostat, made sure the heat pump is clean and free of debris and cleared away any grass or anything.

I would like to fix this but I wanted to ask for advice on my 3 ideas on what to do. Should I...

  1. Replace the thermostat? My partner had trouble with theirs in the winter (it was running all the time) and replacing the thermostat helped there. I was wondering if doing the same would help me.

  2. Call out an ac repair person?

  3. Understand that it is hot and over 90 degrees and this is just how it is and suck it up? (I understand that heat pumps can realistically only cool about 20 degrees and may struggle with the new higher temps in the Summer)

I really appreciate your time and advice.

Thank you

isherwood
  • 158,133
  • 9
  • 190
  • 463

6 Answers6

13

If the system is running (fan is blowing; condenser/compressor outdoors is running) then replacing the thermostat won't help any.

You've done well checking the filter and ensuring the outdoor unit is clean and clear of debris.

One other simple thing you can check is whether the coil above the furnace is freezing. Easiest way to do that is to look at the condensate drain after the system has been running a while. If there are drops or a small drizzle of water exiting then it's working; if the drain is dry then ice on the coil is likely. Ice means blockage of airflow, which means reduced ability to cool.

A system does have its limits; there does come a point at which the system can't cool any more and the indoor temperature will rise together with the outdoor temperature. It's tough to say whether yours is at that point; you'll probably need an on-site service person to evaluate that.

Greg Hill
  • 35,866
  • 42
  • 91
8

It depends. If the A/C has a mechanical problem, have it fixed. You'll know soon enough, if it suddenly got worse.

If the A/C is working properly and simply has never been able to adequately cool your house in these very high temperatures we are now experiencing, then you have 3 options.

  • Suffer.
  • Get a larger or supplemental A/C unit.
  • Cool your house with the power of your brain. I.E. learn stuff about thermal mass, energy storage, insulation and air leakage (to see whether this trick is worth doing) and then pre-chill your house so the mass of the house is nice and cold before it starts becoming unbearable. Then you can - well not quite coast like in the video, but certainly reduce the need for the system to work so hard between 4 PM and 10 PM. Also good for the energy grid's stability.
Harper - Reinstate Monica
  • 313,471
  • 28
  • 298
  • 772
6

It's not the thermostat: it just command call for cool (temp > set-point + hysteresis ) or "stop" if temp < set-point - hysteresis.

So if the AC starts and stops the thermostat is fine.

My ideas are:
• dirty condenser (if you can't see trough, wash it with water, avoid pressure wash, going the opposite direction as air, if you still can't see trough, call a tech and have it properly cleaned)
• dirty evaporator (causes low flow at vents, call AC tech)
• dirty filter (replace it yourself, its cheap and easy, also improves air quality inside)
• low refrigerant (call AC tech)
• undersized unit (deal with it or have the unit replaced with a bigger one)

You did whay you could, call AC tech to check pressures and clean the evaporator.

At last: Check you dont have "economizer" open => these allow air change but waste lots of cool, closing them will keep the cold in.

DDS
  • 2,402
  • 11
  • 15
5

If you have a large external unit, check that the air is blowing in the right direction:

enter image description here

Air is supposed to come out the top of this unit. I've had installers that reversed the fan direction and lowered its efficiency by a very large amount.

Call the installers to fix it since it is their responsibility, but it can also be DIY configured if you are inclined.

Nelson
  • 1,905
  • 14
  • 22
3

You have done the simple checks. Now you need to have the system looked at by a service tech.
What you are describing is system that is low on refrigerant. There are other causes of this behavior. A tech will need to inspect the system to determine what the issue is. You can play detective, but you will still need a tech to fix it. (Special equipment is needed.)

Dug
  • 31
  • 1
-3

Have someone come out to inspect and clean your air ducts. Make sure you go with a legitimate company.

EDIT:

Not sure why the down vote, so here's a link to EnergyStar.gov showing that repairing and cleaning will help.