I’m installing two new ceiling fans below an existing ceiling that cannot be disturbed because it’s decorative, so I’m framing a new drop ceiling cavity consisting of 2x4s to run 14/3 cable and set the two fan junction boxes with steel brackets.

Can I run the cable loosely in this space, connecting only at the boxes, or does this wiring have to be secured somehow? I'm in Kansas and NEC applies.

FreeMan
  • 48,261
  • 26
  • 101
  • 206
Roger
  • 1

1 Answers1

3

If you can get to the areas, and not running cable through a cavity, the wire needs to be anchored. Since you said you are framing in a new ceiling you need to follow the code for new construction. Staple the wire 8 inches from the box minimum. and every 4 1/2 feet.

Your choice of cable should be rated for the breaker that services it. #14 for a 15 amp breaker, #12 for a 20 amp breaker. The reference from another member to 12/3 cable is good advice. The 12/3 will give wire to power the fan and a light separately. A good idea even if the new fan does not have a light, the wire is there for the future. The 12/3 can be used with a 15 or 20 amp breaker.