I am installing a new Whirlpool Double wall oven and a separate cooktop range in a new remodeled kitchen (converted the carport into huge new kitchen). When I installed the wiring, I thought the oven was going to be a 50 amp (based on research before the oven was purchased) and so I ran 6/3 wire for the oven and 8/3 wire for the cooktop. Now that I have the appliances purchased and in the kitchen ready to be connected, I can see that both of them are just 40amp. I have separate 40amp breakers in the box for them. Is there any issue with the 6/3 wire being used on the 40amp circuit for the double oven?
Asked
Active
Viewed 976 times
1 Answers
4
You can use the 6/3 with a 40 amp breaker, just fine.
The breaker protects the wire. Wire can be oversized to the protection of the breaker, but not undersized.
You are fine.