I'm moving in to a house with a Vista 128BPT burglar alarm and I'd really like to add smoke/heat and CO detectors to the system.
However, I also really want the smokes/heat detectors to be on individual zones, or at least zoned per floor - it's 3-level house plus attached garage, with gas HVAC units in basement and attic. If the system triggers, I really don't want to have to search the whole place to find which one tripped.
I know that Honeywell makes a V-Plex addressable smoke that I could use (5193SD), but it doesn't have a built-in sounder and I would really like to avoid having to also install separate sounders, both in terms of having to pull more wiring and in terms of having yet another thing sticking out of the wall/ceiling.
I understand that if I set up 4-wire smokes/CO as separate zones, (1) I'd use a single trigger relay to reset them and it would likely cause a trouble on all of the zones that weren't faulted but got reset, and (2) I'd either need an EOL relay on every zone, or to use smokes with built-in EOL relays (only a few I could find, and rather expensive), or to run 5+ conductors to every smoke so that I could home-run everything but still daisy-chain the power. I also understand that to get one-go-all-go with this setup I'd need a reversing relay (e.g. System Sensor RRS-MOD) driven from a relay on the panel (4204 relay module) and programmed to trigger the relay when any of the fire zones fault.
Is this all crazy for a residential setup? Is there a simpler/more straightforward way to achieve my goals, which are in order:
- Know exactly which detector faulted
- One-go-all-go
- Detectors with sounders built-in