5

I have a 40A double-pole breaker feeding 6 AWG aluminum(?) wire going to a NEMA 14-50 receptacle for an existing electric range/oven. We had the oven replaced with a dual-fuel model (Bosch HDI8056U) that has gas burners while using electric for the oven elements. The manual and rating labels all say "30 amp" but that appears to be a minimum value. I can't find any reference to whether or not a 40A circuit is acceptable for this application. The installer did not seem knowledgeable in this area; he just slapped a range cord on it and went on to the next house.

Is the 40A breaker still okay here, or should I swap in one that matches the "30A" value printed on the oven? If I do switch the breaker, do I then have to change the receptacle/cord to a 14-30 to match?

Location: NC, USA.

smitelli
  • 641
  • 1
  • 7
  • 15

4 Answers4

7

In general, if the installation/operating instructions specify 30A, then using a larger circuit breaker is not fine.

For other types of equipment (heat pumps are typical) the manual may specify both "Mininum Circuit Ampacity" and "Maximum Overcurrent Protection Device" with different values.

Since you say:

The manual and rating labels all say "30 amp"

30A rules. The thing has been tested and listed for failures while connected to a 30A breaker, not for being connected to a 40A or 50A breaker.

So, to do it correctly, you need a 30A breaker, the same wiring (assuming it's actually got a ground wire - there's a whole other mess if dealing with old NEMA-10 and no ground - but if your NEMA-14 is correctly wired you have a ground) and a 30A receptacle (or just skip the receptacle and cord and hardwire the connection in a junction box, which is in many ways preferable.)

Be sure to use a torque driver to tighten connections to the proper specified torque value - that's particularly critical if the wall wiring is aluminum.

You might also drop a note to the LAHJ regarding the installer and their employer Doing It Wrong.

I suppose a potentially acceptable alternative would be to install a fused disconnect behind the stove with 30A fuses. This might cause confusion if the fuse blows, since the breaker would not trip, most likely. If you forgot it was back there, or the next owner didn't know it was, it would be baffling for a while. It's also (IMHO) somewhat less safe than a two-pole breaker where either leg faulting will shut off both poles.

Ecnerwal
  • 235,314
  • 11
  • 293
  • 637
4

The National Electrical Code states in article 422 (Appliances), section 11 (Overcurrent Protection), part (E):

(E) Single Non–motor-Operated Appliance.
If the branch circuit supplies a single non–motor-operated appliance, the rating of overcurrent protection shall comply with the following:
(1) Not exceed that marked on the appliance. [No overcurrent is marked.]
(2) Not exceed 20 amperes if the overcurrent protection rating is not marked and the appliance is rated 13.3 amperes or less; or [Appliance is rated 30A > 13.3A]
(3) Not exceed 150 percent of the appliance rated current if the overcurrent protection rating is not marked and the appliance is rated over 13.3 amperes. Where 150 percent of the appliance rating does not correspond to a standard overcurrent device ampere rating, the next higher standard rating shall be permitted.

40A < 30A*1.5 -> You are fine, factually and regulatory.

2

The Product Specification sheet says "Fixed connection (no plug)" but the installation manual, which includes details for both gas (120V 15A) and dual fuel (240V 30A or 208V 25A) models includes instructions for plug connections and for hardwired connections.

So it may be OK to use this plug/cord/receptacle connected. But it is a $3,000 beautiful machine (dual fuel gets you the best of everything, IMNHO) so why not hardwire it? That avoids the very common problem of mismatched receptacle type (30A? OK, just change the breaker...and now you have a 14-50 receptacle with a 30A breaker and the next machine in 15 years is an induction model that needs more power and gets installed plugin to that without checking breaker size and keeps nuisance tripping (and wearing out...) the breaker until the breaker starts having problems...) and avoids a critical hidden common point of failure.

  • Replace the 40A breaker with a 30A breaker
  • Install a proper 40A rated wire whip instead of the cord/plug
  • Remove the receptacle and connect the wires

The one catch is that you have aluminum coming from the breaker and copper from the range. So you need a proper way of connecting 6 AWG aluminum to 10 AWG copper. The Ideal 65 Purple doesn't handle large sizes. Polaris connectors may be your best bet:

Polaris

Depending on breaker brand (and you must use the correct type for your panel), you may need Polaris (or similar) connectors to pigtail 8 AWG aluminum or 10 AWG copper wire to the 6 AWG aluminum wire in order to fit on the breaker.

manassehkatz-Moving 2 Codidact
  • 139,495
  • 14
  • 149
  • 386
2

Change the breaker to 30A. The instructions are part of the Listing, and the NEC requires following them.

Sometimes you have to figure out how to comply with multiple code sections, here at least 3 have to be considered. Section 422 deals with appliances:

NEC 422.11(E) Single Non-Motor-Operated Appliance. If the branch circuit supplies a single non-motor-operated appliance, the rating of overcurrent protection shall comply with the following:

(3)Not exceed 150 percent of the appliance rated current if the overcurrent protection rating is not marked and the appliance is rated over 13.3 amperes. Where 150 percent of the appliance rating does not correspond to a standard overcurrent device ampere rating, the next higher standard rating shall be permitted.

You also have to go back to the beginning, section 110 Rules for Electrical Installations:

110.3(B) Installation and Use. Equipment that is listed, labeled, or both shall be installed and used in accordance with any instructions included in the listing or labeling.

UL/CSA/ETL Listings require installing and using as instructed in any enclosed instructions. Page 11 of the instructions shows a table, says 30A for 120/240v ranges. 30A is less than the maximum of Section 422, so only a 30A breaker complies with both Sections 422 and 110.

The receptacle can remain a 50A:

NEC 210.23(B)(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

A 50A receptacle is not less than 30A, so satisfies the reqirement when it is a single receptacle on a branch circuit.

There is some confusion about the receptacle rating, eyes are drawn to an irrelevant table, 210.23(B)(3). The table for years was titled "Receptacle Ratings for Various Size Circuits", it shows a 30A breaker only allows 30 receptacles. But the table doesn't apply! Section 210.23(B)(3) only applies to circuits with multiple outlets. The 2023 edition of the NEC makes this more clear, the name on the associated table has been changed to clarify to now read "Receptacle Ratings for Circuits Serving More Than One Receptacle or Receptacle Outlet".

NoSparksPlease
  • 20,598
  • 2
  • 21
  • 51