Single family home built in 1987. Question is regarding the as-built: Is it grandfathered and does not be updated?
There is no neutral-ground bond in the 100A breaker equipped main service disconnect located outside next to the meter box. Only the ground cable to the service panel and a cable to a ground rod are present on a box bonded terminal bar in this box. The neutral just goes thru the service disconnect box, not terminated to anything, going on into the separate meter box.
There is a neutral-ground bond in the garage main lug 20 space service panel, consisting of a #6 copper wire between separate neutral and ground bars.
There is a 2-2-2-4 service entrance cable run from the disconnect box to a service panel in the garage, not in conduit.
Since there is only 1 neutral-ground bonding point the intent of NEC code that no neutral current can flow in the grounding system under normal conditions is satisfied. It just is not bonded where the 2008 and later NEC book says.
My question is since this pre-dates 2008 NEC and there is no new electrical work happening is this grandfathered? Any safety concern?
Addressing the questions in comments:
The meter, outdoor box w 100 main breaker, and the 20 space main lug breaker box are all on or in the same building, a single family residence.
The metal outdoor box is unlocked and has a 100 Amp 2-pole breaker. That is the means of service disconnect as well as the protective device for the entrance cable. It is located outside adjacent to the outdoor service meter box.
The inside box is a main lug 20 space 2-pole load center with separate ground bar and neutral bar. It is located in the residence's garage.
The connecting cable is a 2-2-2-4 copper conductor entrance cable, not in conduit. Approximately a 50' wire run inside walls and across attic.
The outside box has an AC Disconnect label on its door.