I have a 1961, Apartment with Bolted on panels vrs the Stab-lock is bolted on safer?
Asked
Active
Viewed 89 times
1 Answers
4
If you are talking about Federal Pacific Electric in both cases (bolt-on and snap-in, both exist under the "Stab-Lok" name), the whole thing needs to be replaced promptly either way. The internal mechanism has several problems according to http://fpe-info.org/hazardous_fpe_171110.pdf which has nothing to do with the bus connection method:
- Breakers often don't trip at their rated current, but at a much higher level, which can lead to fires
- Breakers can jam on overcurrent and not trip at all, which can lead to fires
- Breakers can jam when manually moved to "off" which is a safety problem and also possible fire hazard
Some (probably not all) of the bus-connection problems may be mitigated by the bolt-down breakers, but that does not make them acceptably safe. Either way, these panels are a fire hazard and need to be replaced promptly.