Some kinds of loads take in more energy than they're going to need during part of each AC line cycle, and then feed the excess energy back into the power mains during another part. Such loads are called "reactive loads", and can be subdivided into capacitive loads and inductive loads.
If one were using an extreme capacitive load on one leg of a multi-wire branch circuit and an extreme reactive load on the other, it would be possible for the RMS neutral current to exceed the RMS current on either leg. In general, however, the loads that are most reactive tend to operate with relatively small levels of current. An LED-based night light with a capacitive dropper circuit may have 0.05A load that is almost purely capacitive, and an electric clock motor may pose a 0.05A load that is almost purely inductive, and plugging one onto each leg of an MWBC may result in a neutral current that is greater than 0.05A. On the other hand, even if the neutral current were 50% greater than the higher leg current, that would still only represent 0.075A--nowhere near enough to pose any kind of overload risk.
If one were to plug enough capacitive-dropper night lights on one leg and enough motorized electric clocks on the other, it might be possible to make the neutral current slightly exceed 15A while keeping both legs under 15A. In practice, however, such an imbalance between capacitive and inductive loads would almost never occur in any realistic scenario, and even if it does the neutral current would be only slightly greater than the higher leg current.