I'm trying to replicate the battery backup setup described in this video and in text below. I'll state what the video demonstrates, then share the parts and plan I have. I'm looking for input on how correct and safe my plan is.
In the video I based this on, someone DIY's an inverter-charger UPS type of power backup system, which has benefits of lower total cost and easier to maintain (you can replace components rather than entire system). Since I have some components already, this is preferable.
In the video they connect a PROwatt SW inline transfer relay to 120VAC household circuit sufficient for the sump pump, and to a 12VDC-120VAC inverter, then on the other end of the transfer relay they have the sump pump. The inverter is connected to a 12VDC battery, which is connected to a charger plugged into 120VAC.
Here's my plan:
There's a 20A 120VAC circuit for a sump pump, with one duplex receptacle on it.
I have a 12VDC LiFePO4 battery and plan to expand capacity with more of them in parallel, and I have a compatible Victron BlueSmart IP65 Charger (12 VDC, 15A). The battery would connect to the charger, charger plugged into the 20A 120VAC household circuit. That's my DC power supply, which I figure the Smart Charger can always keep topped off and not over-charged so long as mains power permits, while also safely isolating the DC power from the mains power supply.
Then I'll get a 2000W pure sinewave inverter with GFCI receptacles to supply the 900W sump pump (rated at n more than 7.6A continuous draw at 120VAC). I expect the inverter, battery, and charger would always be 'on' and simply not drawing much from the battery while keeping it topped off, so long as AC power is on. My understanding is there should also be a 15A fuse between battery and inverter, and there should be a ground from the inverter to the house's ground copper.
To put the sump's load on the inverter+battery only when AC power fails, I'd use a transfer relay. Sump plugs into transfer relay, transfer relay plugs into house's AC and into inverter's DC power. This would act as a switch so that no load is on the inverter unless a load is generated that AC power cannot supply. The PROwatt SW model linked to above seems fine. That said, I'm not experienced in DC to AC connections (I have decent familiarity with AC and amateur familiarity with DC systems).
I understand the DC leg of this system is rated to 15A because the charger, inverter, and transfer relay are all rated for 15A. For that reason, I figure I need a 15A external fuse between the battery and the inverter on the hot wire to make sure the load on the battery does not exceed that amount. (The inverter I'm looking at has 15A GFCI receptacles and an internal fuse, as well.)
For the AC leg of the system, I don't see a reason why higher amps rating would be a problem. The 20A duplex receptacle and circuit (wired with 12/2 cable and 20A breaker) should be able to handle any 15A loads coming from the DC system (via the charger's load), and the 20A circuit was designed to be more than enough for the sump pump load directly.
Are the parts and ratings I described all compatible? Is there any parts missing or areas of concern I didn't address?