I am installing some architrave power sockets into a garage ceiling, so I have flexibility to move light fixtures around.

Country is New Zealand, and the line voltage specs are 230V AC 50 HZ.

I have run 1.5mm2 cable, but there are points where I want one socket to have two wires, an incoming and an outgoing.

I have been using the correct size ferrule, but now I want to put two wires under one screw.

Do I put two wires into one larger ferrule? enter image description here

OR Do I put two ferrules under one screw? enter image description here

Wire nuts are not an option here - I could pigtail out to a three-way joiner, but that needs its own junction box.

What's the best way to do this? Extension question, what if there were more-than-two wires coming to the same point?

Criggie
  • 11,950
  • 2
  • 26
  • 79

1 Answers1

2

I am installing some architrave power sockets into a garage ceiling, so I have flexibility to move light fixtures around.

Batten sockets are more usual in that application.

SFAIK ferrules are not required (although this may have changed since I last looked), If you are going to use them put all the wires into a single ferrule.

1.5mm2 seems kind of skinny for outlets. (but this is a lighting circuit, not a GPO circuit, so assuming 10A breaker or smaller this is fine)

You are absolutely allowed to use those holes to join multiple wires, this is why they are 5mm diameter.

Jasen