tl;dr - Would we expect an amp drop between the SEU-AL before the disconnect and the copper going to the AC? If not expected, does this indicate an issue? Would AL wire stress a breaker more?
After having the fourth HVAC tech come out to see why my breaker is tripping, he determined that the actual AC seemed to be working correctly and then proceeded to start over checking everything in detail.
While I had visually checked the breaker (with case off), I did not remove it because I didn't want to risk mistakes. The Tech took the breaker out and when he held it, he said it was way too hot; it also stayed hot to the touch for several minutes after being replaced. I had already purchased a replacement breaker just in case, so he switched it and it was not causing an issue. From the breaker to the external disconnect box for the AC is 6 AWG SEU-AL wiring.
He took amp readings at the breaker box and then outside and was getting slightly different readings. He then took readings right at the disconnect with the wires next to them and he would observe the difference pretty much at the same time of about 5 amps.
He called a few people including his boss and an electrician with which he works. While he never saw the amps at the AC condenser ever go over the limit on the name card, nor did he see the amps on the breaker go above their trip value, his conclusion was that possibly the AL wire was in some way beating on the breaker (if the breaker just didn't go bad on its own). He checked inrush and running amps and didn't see the amp draw going too high.
We had the discussion about how copper is better, but they probably went with AL to save money, its possible safety implications (though this isn't a 70s house and this was to a disconnect, not a device), etc. For more discussions about AL being used in this situation, see this question. His final recommendation was that he didn't see anything immediately dangerous or broken, but to check/replace the breaker every few years in case there is something about this system that is causing the breaker to go bad. Maybe there is something bad with the wire in a finished part of the basement through which it travels on its run.
My questions therefore are:
Would we expect that, essentially right next to each other, the amps on the AL would be like 17, while the copper would be 12? (See photo below for what I am talking about). Should the amps be consistent across the circuit or will it change based on the conductor / wiring
Would using SEU-AL from the breaker to the disconnect cause more stress to the breaker? Does this make sense or is it more likely just a bad breaker, a surge happened at some point, etc.
In reading about the history and code around Alumninum, I saw several things about the importance of properly torqueing the connections. The Tech seemed to really tighten everything up by hand when he saw a screw, but does this mean something else / what do I check?
UPDATE
Original photo was labeled wrong.
Since I have a clamp meter now, I took my own readings at photos. I will also add that while trying to clamp each running wire, when I tried to clamp the two on the left, I couldn't do it while running because the wire would move and spark at where it was screwed down on the disconnect. When the AC guy was here, there were also sparks. I am not sure if that is expected some times or also something to consider. I compared the disconnect to my other AC system and you could see the other one was nice and clean and this one had singe marks; though of course when plugging the other disconnect back in I also didn't get it quite right and it sparked.
As for the photos. I took the photos of the two on the right without disconnecting because I could clamp. For the two on the left, I pulled the disconnect each time before clamping to then get the reading. I took a few readings and the numbers were about the same on each wire. I was not sure if I needed to check something on the ground wires, but I didn't see a good way to get them. I also learned that there are amp ratings on the disconnects themselves, these are 60amp boxes if that makes a difference.
Is the box replacement a good step to consider? Is this something I can do myself if it just disconnect the power? or should I call an electrician at this point?
Is there usually some play where the disconnect connects the wires or should they be in so tight then when I move them around to clamp they should not have moved at all.
The theory is that the amps are going somewhere via the disconnect? It is not something on the AC unit otherwise it would still read the same at the disconnect, the drop would be on some split leg later. Is it possible it is just going to ground? i.e., the problem is probably "at the disconnect" or the "disconnect itself"?
Close up of all connections, anything obviously visually wrong?

Right most (from breaker), 15.4:
Right center (to AC), 11.07:
Left center, 15.17:
Left most, 15.28:
second reading, right most 15.23:
second reading, right center 10.89:
disconnect prongs: Something that is just going to happen with pulling it in and out so many times? Or something to be concerned about. The disconnect on my other AC was perfect until I put it back it after trying to get a comparison photo and it was the same - no issues with the other unit
Update 2
Based on some comments, etc. below I redid my reading today. I ensured the clamp was fully closed. Guess what my readings were on the AC line, ~15 amp. I unclamped a tiny bit, and guess what ~10 amps. Thanks for the people looking carefully at the photos! I guess the HVAC tech must have done the same thing and not noticed, so when I got the same readings on my own I didn't assume a problem with the measurements.
What an unnecessary roller coaster ride, but at least something that didn't make sense was resolved with something that did make sense.
I am still concerned about the disconnect given how beat up it is and added a few more photos. I see some burns, but probably from the arcing/sparking after the fact? I will also invest in a torque driver (cheaper than another service call leading to nonsense) and ensure everything is tight.
At the end of the day, maybe it really was just a bad breaker? Haven't had another trip since we changed it, but will need to let is run and take over the cover again to feel if it gets hot.
Photos of the readings as of a few minutes ago ensuring the clamp was done correctly:
Center-right to AC:
I also went from the right outside to right center ensuring the clamp was correct and got pretty close readings. Perhaps since nothing is wrong now I can assume its all okay?
For good measure photos up close of the disconnect: