I recently helped my son-in-law install a ChargePoint Homeflex level II EV charger in his garage. It draws 48 amps max and we have it hardwired with #6 AWG THHN to a 60 amp breaker. He would like to install a 7500 watt Tempware forced air electric heater (https://a.co/d/0WoNGj9) in the same garage. It draws a maximum of 32 amps and recommends a 40 amp breaker and 8 AWG copper wire.
We would like to run it off of the same 60 amp breaker as the EV charger and avoid having to run a separate circuit from the other side of the house. I realize that the combined load would exceed the capacity of the 60 amp breaker and the #6 AWG copper but individually they would be within NEC requirements. He only uses the EV charger overnight when costs are the lowest and plans to use the heater during the day or early evening.
My question is:
Can we split off the existing line running to the EV charger with a 240 volt A-B option switch in the garage that would isolate the EV charger when the Tempware heater is running and vice versa when the EV charger needs to run?
There may be another option for a small sub panel in the garage feeding off the 60 amp circuit which was recommended in a similar question but I doubt that is workable within the NEC in this situation because the individual circuits need to be isolated.
We're open to any suggestions.