Four wires: black, red, blue and white
Black and red are for a 30a dryer.
Blue is for 120v/20a circuit. All #10 gauge. Can the neutral be used for both circuits?
Four wires: black, red, blue and white
Black and red are for a 30a dryer.
Blue is for 120v/20a circuit. All #10 gauge. Can the neutral be used for both circuits?
No, for circuit that have a neutral there must be one neutral for each breaker. you can share grounds, but you can't share neutrals.
The way to think about it is to pretend that every circuit is protected a GFCI device, which isn't far from the truth in new construction. In order for GFCI to work, all hots + neutral in each circuit must be balanced. The 30A two hots and neutral are balanced. The 20A hot and its neutral are balanced. But if you combine the neutrals then there is no way to send just the right amount of current to each GFCI.
Note that this is per circuit. A circuit can be:
An MWBC might be where you get this idea of "share neutral". But an MWBC doesn't share a neutral between two different circuits. It is really one circuit, despite the historical situation of using two separate breakers instead of a double breaker. Technically, an MWBC can still be two separate breakers, as long as they are next to each other and handle-tied. But a new MWBC in an area that requires GFCI (e.g., kitchen, bathroom, laundry room, garage) has to be a double breaker in order for the GFCI to work.
If these wires are in conduit then just add a 12 AWG neutral. If these wires are part of a cable then you need a separate cable for the 20A circuit, but that can be a 12 AWG /2 instead of a 10 AWG /4.