This forum has extensively fielded questions on the requirements for interconnecting the home electrical system with a portable generator with an intact neutral-ground bond. From what I can recall, the options seem to be to sever the generator’s neutral-ground bond or to utilize a neutral-switching transfer switch.
As I was daydreaming about purchasing an F-150 Lightning and cord connecting the onboard 240V/30A power socket to a hypothetical generator inlet at my service panel, I came across the fact that the F-150 Lightning has GFCI protection on all its receptacles. This would not play nice with the neutral-ground bond in the service panel since it would allow normal operating (non-fault) current to return down both neutral and ground paths back to source, tripping the Lightning’s GFCI.
Now whether using a Lightning or a bonded neutral-ground generator to power the house, I am wondering: does code permit one to wire a 240-to-120/240 isolation transformer between the generator inlet and the service panel, thereby serving the panel with a newly regenerated floating neutral?
The potential benefits being agnosticism to these details of the supply source and the ability to use a simple sliding plate interlock across the supply breakers in the service panel.
Perhaps one issue is, unless properly sized, the transformer can’t necessarily flow the current necessary to magnetically trip the source’s breaker in a secondary-side bolted fault to ground scenario?