Five years ago my electrician installed a Stelpro DRI0521W Dragon ceiling fan heater in my garage. It has a load of 20.84 amps. He installed a 30 amp breaker and told me that he used 12 AWG for the wiring.
Two days ago I caught the heater running endlessly and the garage smells like fire. The breaker did not trip.
I tripped the breaker manually, unscrewed the thermostat and, sure enough, the wiring had overheated and burned right through the insulation in multiple places.
I am not an electrician, but here is my understanding of what is going on...
- The heater draws 20.84 amps.
- Therefore, the wire should be rated to carry at least 20.84 * 1.25 = 26.05 amps
- The 30 amp breaker did not trip because the load did not surpass 30 amps.
- The load did not surpass 30 amps because the wire melted before it could do so.
To prevent a fire, I need to use a wire which is rated for at least 30 amps. Per my understanding, I need to either use a 10 AWG wire with a temperature rating of 60°C or a 12 AWG wire with a temperature rating of 90°C.
Given that the wire burned through the insulation and the breaker did not trip, it seems to imply that the 12 AWG wire does not have a temperature rating of 90°C. When I ran this line of reasoning by my electrician, and suggested that we might need to use a 10 AWG wire, he texted me back:
Yea but not for heating.
What am I missing here?
Could the overheating wires have been caused by a defective thermostat, and does not necessarily indicate a problem with the wiring?
Let's look at the photos...
On the one hand, the melted wire nut indicates a possible faulty connection:
On the other hand, there is melted insulation away from the wire nut:
Then again, the wire nuts were shoved into the back of the junction box. If it overheated while being folded in like that, it is quite likely that it was touching those parts of the wire and caused their insulation to melt.
Thoughts?