I’m redoing the electricity at my cottage, which is a house on stilts. The main trajectory of the cables will be from the breaker box, down in the crawl space (which is vented and enclosed only with plywood, no foundation walls) and back up in the walls to the outlets.
I plan on running T90 conductors (the canadian equivalent of THHN) in PVC conduit from the breaker box and all through the crawl space to protect the conductors from rodents. A junction box will end the conduit run and house a T90 to NM connection. The NM cable will then leave the junction box and enter the wall until it reaches the outlet.
Does this make sense. Any better ideas? Should I do things differently?
Thank you.
spuck
  • 1,960
adam
  • 107
The junction boxes cannot be hidden, so your plan will be ok if the T90 to NM connection is in an outlet or switch box or an accessible box with a blank cover.
RMDman
  • 52,615
  • 113