I am replacing an electric range with a gas range. The electric range is wired with 3 wire 8 gauge on a 40amp breaker.

For the gas range I need a 15amp circuit. Can I just wire nut off red wire and change the breaker to a 15amp? The question is the I am not sure if the #8 wire is too heavy for the light 15amp load?

isherwood
  • 158,133
  • 9
  • 190
  • 463
Collins
  • 1
  • 1

3 Answers3

5

As @RMDman pointed out, #8AWG will easily carry a 15 amp load. Looking at a Square D and a Cutler Hammer CH breaker, both are good for AL/CU #8 to #14 wire. You can always get some #14 wire and splice it to the #8 and connect the #14 to the 15 amp breaker.

JACK
  • 89,902
  • 21
  • 80
  • 214
2

They sell these UL-listed adapters with integrated fuses which would technically work with the 40A breaker in place as the integrated fuse would provide the OCP you would need. I would still change out the breaker out of precaution though, just pigtail the #8

https://www.menards.com/main/electrical/electrical-cords-surge-protectors/outlet-adapters/woods-gas-range-adapter/548303/p-1513154689979-c-6483.htm?exp=false

cluelessone
  • 329
  • 1
  • 9
-3

It will work but you’re suppose have a ground and neutral.

If it were my house I would repurpose the red wire as the neutral in the panel and in the receptacle.