6

I need to run a 50 amp circuit (120/240V) from a shed to a travel trailer that is permanently in place.

The previous trailer had 30 amp 120V service running underground to a mounted/covered outlet under the trailer and then the standard trailer cable/plug into that.

The run is ~50 ft. Running the 30 amp 120V service was fairly straightforward (big box hardware stores have the right wired for burying). But when I start looking at 50 amp things get less straightforward (to me).

I'm assuming from a brief googling of big box stores have not resulted in any results for #6 non-conduit buriable wire. So this leads me to believe that I need to run it in conduit, but then I get concerned about heat (this may be an incorrect understanding).

We only occupy the travel trailer 2 - 3 days a week for May/Jun/Jul/Aug/Sept. Most of the days are spent outside and the AC & oven will rarely be used. (I understand that you should plan for the largest load not smallest).

Can I run 50 amp (120/240V) underground? Do I need to ground the chassis of the trailer to a 8ft grounding rod? Should I use #4 instead of #6 to reduce the heat concern?

Niall C.
  • 20,909
  • 19
  • 95
  • 135
Wayne Arthurton
  • 163
  • 1
  • 1
  • 5

1 Answers1

11

Cable

The cable you're looking for is Type UF, or Underground Feeder cable.

enter image description here

It can be purchased at big orange, and big blue, by the foot. It's available in 6/2, 6/2 with ground, 6/3, and 6/3 with ground, and is rated for direct burial.

Attachment to Service

There is one temporary, and two permanent ways to supply power to a park trailer.

Temporary

Power-Supply Cord

You'll want to use a NEMA 14-50 receptacle, and 4 wire cord with NEMA 14-50 plug to connect the trailer to the service. The trailer's electrical grounding will be through the service plug, so only the distribution panel will have to be grounded.

enter image description here

Permanent

Mast Weatherhead

You can use four continuously insulated, color-coded feeder conductors strung from a mast to a weatherhead as a permanent feeder.

enter image description here

Raceway

A metal raceway, rigid nonmetallic conduit, or liquidtight flexible nonmetallic conduit, from the disconnecting means to a junction box on the underside of the trailer can serve as a pathway to run permanently attached feeders.

enter image description here

NEC

For reference, park trailers are covered in article 552 of the National Electrical Code.

Tester101
  • 133,087
  • 80
  • 327
  • 617