I am wondering if I'm using a 10/3 teck cable to power two 20 amp GFCI receptacles for a temporary power situation, can I use two separate single pole 20 amp breakers at the panel for each receptacle. Meaning i took Black wire to one receptacle, Red to other receptacle and pigtailed neutral and shared it between receptacles.

Will it work? Why or why not?

Is it to code?

Tester101
  • 133,087
  • 80
  • 327
  • 617
Joe
  • 21
  • 1
  • 2

1 Answers1

2

I'm not sure what the codes are like in Canada, but here in the US the only problem you'll have is that you're using two separate breakers. Thought the problem can be overcome by installing a handle tie, to link the breakers together.

As for wiring the GFCIs, a diagram can be found in this answer.

enter image description here