I have a room that has some really ugly cheap panelling on the walls. I want to rip it out & replace with drywall. While I'm at it, I'd like to add soundproofing insulation between rooms & thermal insulation on the outside walls.
However, the house has knob & tube wiring. Is it safe to leave the wiring alone for this project? (Obviously if something must be done, doing it when the wall is open is best.)
  • 20,909
  • 95
  • 135
tomwhipple
  • 181
The answer changes depending on location.
Because of a complete lack of actual fire incidents, four Western USA States: CA, OR, WA and ID petitioned for an exception to NEC 394.12 and permit insulating over Knob & Tube Wiring. In some places you must first file a Knob-and-Tube Wiring Safety Report, and everywhere else it's a good idea.
It is a complete myth that Knob & Tube must be air cooled. Instead measure the gauge of the wire and put in an appropriate AFCI breaker for the gauge, and you're done. 100 year old copper is just as good as modern copper, in regards to household use. You should remove from the K&T any high load devices. What's left, especially in the era of CFL's and LED's, won't draw enough current to cause a problem.
The insulation of the era was not all that good, and perhaps for that reason K&T does not depend on it. Ceramic tubes will outlast civilizations, and hold the wires apart even if the insulation is damaged.
You can even add an extra margin of safety by underrating the K&T (the opposite of depending on air cooling). For example if you find 12 gauge wire, put a 15 amp AFCI in place, and you're more than done. For 14 gauge wire, a 10 amp breaker might do nicely, even if they look at you funny at Home Depot. Home Depot probably won't have the right breaker, but you can brave DIY scorn at Grainger, or just order online.
See
You should, however, replace any fuses. Those are dangerous, even with Type S fuse bases.
Bryce
  • 11,057
  • 77
  • 120
If you can insulate the walls without a "material that envelops the the conductors", then sure. But I would think that wouldn't be a very well insulated wall. Knob and Tube wiring is meant to have an area of free air about it. Insulation encroaching on this space could cause the wiring to overheat.
National Electrical Code 2014
Chapter 3 Wiring Methods and Materials
Article 394 Concealed Knob-and-Tube Wiring
II. Installation
394.12 Uses Not Permitted. Concealed knob-and-tube wiring shall not be used in the following:
(5) Hollow spaces of walls, ceilings, and attics where such spaces are insulated by loose, rolled, or foamed-inplace insulating material that envelops the conductors