17
We have an unfinished attic - the insulation-everywhere, step-in-the-wrong-place-and-fall-through-the-ceiling kind.
I'd like to run Ethernet cable through the attic. I know for Romex, I'd have to staple the wire to the joists, drill holes when running perpendicular, etc. However, I can't find anything stating I need to do the same with Ethernet. In fact, much of what I've read online implies there are basically no rules for Ethernet!
So I want to make sure:
  • Do I need to need to staple the Ethernet to the side of the joists? Drill holes when running perpendicular? Can I simply set the cable down along the top of the joists?
  • If I decide to use conduit (for future-proofing), do the rules change?
  • If I were to run the cable through the dropped-ceiling of a finished basement instead, would the rules change?
5 Answers5
18
National Electrical Code 2014
Chapter 8 Communications Systems
Article 800 Communications Circuits
I. General
800.24 Mechanical Execution of Work. Communications circuits and equipment shall be installed in a neat and workmanlike manner. Cables installed exposed on the surface of ceilings and sidewalls shall be supported by the building structure in such a manner that the cable will not be damaged by normal building use. Such cables shall be secured by hardware, including straps, staples, cable ties, hangers, or similar fittings designed and installed so as not to damage the cable. The installation shall also conform to 300.4(D) and 300.11.
Chapter 3 Wiring Methods and Materials
Article 300 Wiring Methods
I. General Requirements
300.4 Protection Against Physical Damage.
(D) Cables and Raceways Parallel to Framing Members and Furring Strips. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed parallel to framing members, such as joists, rafters, or studs, or is installed parallel to furring strips, the cable or raceway shall be installed and supported so that the nearest outside surface of the cable or raceway is not less than 32 mm (11⁄4 in.) from the nearest edge of the framing member or furring strips where nails or screws are likely to penetrate. Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by nails or screws by a steel plate, sleeve, or equivalent at least 1.6 mm (1⁄16 in.) thick.
300.11 Securing and Supporting.
Please see NEC for full text
So basically, you're going to want to protect and support the cables in a similar manner to any other cables. Curiously, the code didn't mention 300.4(A) Cables and Raceways Through Wood Members.. Though I'd likely still follow that section if I had to run communication cables through wood members.
If you run the cable through conduit, you'll have to follow the code for protection and support (fill requirements do not need to be met, per 800.110(B).
If you run through a drop ceiling, you'll have to install support wires for the cable, or support it in another approved manner. You can't support the cable using the ceiling grid, or support wires.
Here's a great document from Mike Holt that explains Article 800 (with images).
Introduction to Article 800 - Communication Circuits (PDF)
The rules for adequate protection of wires from damage, and "workmanlike" installation apply to low voltage (Class 2) cabling just as they do for any other electrical installation.
Yes, you need to have the cable well attached to framing, and it cannot be resting on a drop ceiling.
Conduit is not required, but can serve as both protection and support for low voltage cabling. "Smurf tube" or Non-metallic flexible conduit is often used for this. It is even available in an orange color to signify it contains low voltage wiring.
In general the rules are similar, but more relaxed. Most notably low voltage cables can have junctions exposed to air (not in a box.)
mfarver
  • 1,347
Never posted on this site so sorry if my formatting is off but I noticed this post is still active. I was hoping after 5 years you have gotten the solution you were looking for but to shed some light on this in simple terms. Click on the link of the Mike Holt document on Article 800 of the NEC the other person posted. Reference these parts below:
800.110(A)(1) on page 75: calls out figure 800-24. At the bottom of the figure the text says "Communication cables aren't required to be installed in raceways." which means you don't HAVE to put the wiring in conduit. Sometimes it just makes things easier and/or neat. If you don't put in in a raceway/conduit you have to still support it though, via the section below.
800.113(B) on page 78: which basically tells you what you cannot do. But the author makes a comment, that states you have to secure the cabling to structural components of the building using things like straps, staples, cable ties, etc. that are designed to not damage the wiring. I am not 100% sure on the allowed "unsupported length" but I probably wouldn't go longer than 6ft if possible.
If you are looking for clamps; when I worked on aircraft, we had cable clamps p/n MS21919 that did a great job. They might be overkill for what you need though.
As for the smurf tube. Double check your village code. They might have adopted the NEC but then made amendments to it to not allow ENT (smurf tube). My village requires all wiring within conduit to be in EMT rigid tubing (I hope they only mean for power, and not communications but I have to ask). Also for the color of the smurf tube, I noticed someone else said orange was for communication. I know orange is used for communication when buried but I also look at the Carlon Catalog, page 3 in the "options" and they suggest yellow for communication. So I don't know what is right, only that I'm sure the color will mainly be for your reference only and as long as you know.
tsay40
  • 61
most runs at 48 volts or lower i ack running 3 cables out side cable heavly shealded and weather proof , atic run very hot u need run under ground earthernet as far rest i have 1000 foot cat 6 dosent fall under any code and way this being run code dosent even apply, but common sence dose throw if u get enterprize swich power cut off if cable damage, cheaper swich will burn out that line, i ran cable better much of 30 years and them reg how 48 volt ran over 4 wires out 8 , some points should take dont run next power lines, power lines puts out megnecit feld will interfare with them even if it shelded , there is no ground for these cables the ground comes from end to end swich to device, now if it cisco there router can change voltate to meat the demands, but i dont know anything else that can , and to hotwater line 48 volts once line load is remove power is trun off for it short out would be very cheap swich, i not be concern about code if u running a good poe swich voltate is to low and amps is to low to even bother with and not possable start fire , dont work that way the device it connect to ack has to talk to swich to turn power on once this stops like mice chew throw wire power would be turn off at switch
-2
Depending on your country or local government, if you are having an electrical inspection on your home the inspector will have an “anything goes” attitude about Ethernet and other communication cables. Especially in America.
The only thing they will fail you for is a true violation that is dangerous like damaged cables or cables shorting to 120+ volt lines. Or even cables touching a hot water line.
So if you live in a home and are running a cable or fixing your Ethernet system just use common sense. You’ll probably be okay.