54

In short, most of the outlets in my house have one working receptacle and one that any cord plugged in will immediately slip out of. Some of my outlets don't have any working receptacles (I hope I'm using the right terminology here).

Is there any way I can repair these, or am I going to have to go through and replace every outlet in my house?

Chris Cudmore
  • 14,169
  • 7
  • 61
  • 91
Chris Sobolewski
  • 939
  • 3
  • 9
  • 11

5 Answers5

51

You will need to replace them (or get an electrician to replace them).

Replacing sockets is a straightforward job:

  1. Turn off the power to the receptacle.
  2. Verify that power is off at the receptacle.
  3. Unscrew the old socket from the box.
  4. Make a note of which wires go where.
  5. Remove the wires from the old socket.
  6. Wire up the new socket - double checking that live -> live, neutral -> neutral and earth -> earth.
  7. Screw the new socket onto the box.
  8. Turn the power back on.

This is still a job a householder can do in the UK. However, if you are uncertain about any of the above steps or you think there might be something more serious wrong with the electrics then get an electrician in.

If the plugs aren't holding in the sockets then the sockets are potentially dangerous.

Jay Bazuzi
  • 11,778
  • 34
  • 100
  • 143
ChrisF
  • 16,973
  • 5
  • 51
  • 74
24

Replacing is straightforward. See ChrisF for the details.
However, I just wanted to add the following (Since you appear to be from Wisconsin, I'll assume 120v 60hz wiring) :

1: Standard wiring for an outlet is

  • Black wire - Gold coloured screw. (HOT)
  • White wire - Silver screw (Neutral)
  • Bare or green - Green screw (usually connected to the metal mounting flange)

Get a three pronged wiring tester and test the wiring BEFORE removing the outlets. Put a post-it on any that doesn't test properly. That way, you'll know to check it when you're wiring.

Three things you need to watch for:

  • Chained outlets - This occurs when there are two blacks attached to the hot (gold) terminals. They may be attached to the same screw or a different one on the same side. What is happening, is the hot is being carried over to another outlet or to a switch on the same wall. (same for white) - rewire the same way. BUT - Make sure it isn't a SPLIT!

  • SPLIT outlets - These are most common in the kitchen. There should be two blacks to separate terminals, two whites (also to separate terms) and two greens (to same terminal). The difference here is that there is a small knock-out removed between the screws that electrically separates the upper and lower receptacle. This allows you to wire each receptacle to different circuits, allowing you to plug in the toaster and the kettle at the same time without tripping the breaker. When buying receptacles, ask the hardware guy to show you where the knockout is, and when you remove the old one, check for a split. -- Edit based on comment to another answer: Beware of splits because one outlet may be de-activated at the breaker, but the other could still be live. Always check both outlets before opening.

  • Switched outlets - These usually are splits, with one receptacle wired black & white (always on) and the other wired red or blue and white. The red wire is a switched hot, coming from a wall switch. The knockout should be removed, but they may not be on separate circuits. If they are on the same circuit, they will often only have a single white on the neutral side, and the knockout on the neutral side will not be removed.

If you come across any other creative wiring, call an electrician to sort it out.

enter image description here

Chris Cudmore
  • 14,169
  • 7
  • 61
  • 91
7

In addition to the other answers, here is some advice on selecting receptacles.

  • Choose heavy-duty models. Cheap ones will break sooner, and the contacts will wear out sooner, like your current units.

  • Prefer a contoured face to a flat face. When you go to plug in a lamp at night, or something behind furniture, it's easier if the contours guide the plug in. (If you try to use your finger to find the hole, you can easily shock yourself.)

  • Prefer screw terminals to quick-connect push-in terminals. However, good units let you push wires in the back and then secure them by screwing down to clamp them in place.

  • Consider tamper resistant ("TR") receptacles. Code requires these in many areas today. (They may require replacements in existing work to be TR, too, I'm not sure.) If someone tries to push a knife/screwdriver/paperclip in to one slot, it won't go in, protecting from a shock.

Jay Bazuzi
  • 11,778
  • 34
  • 100
  • 143
3

The only way to repair your receptacles is to replace them.

Chrisf glosses over a point that I consider the key to such a project: "Wire up the new socket".

You have likely never done this before so I want to caution you to make sure you have a good solid connection when connecting the wires to the new receptacles.

Any kind of connection which is loose or can become loose is a fire hazard. With this in mind, I highly recommend you consider the Leviton Spring and Clamp receptacles. They make it much easier to get a good connection. Please see the following article for more details.

http://www.handymanhowto.com/2011/01/17/electrical-outlets-side-wire-versus-back-wire/

It shows you the difference in quality between residential and industrial grade and also why "quickwire" is not as good as the alternatives.

Philip Ngai
  • 3,503
  • 1
  • 21
  • 20
0

Often, contractors use the least expensive materials they can find. That includes outlets. The cheap outlets ($1 USD) often have less metal to press against the plug and so don't hold as well. An outlet for only about twice the price ($2 USD) hold better. This information comes from a wikipedia search and of course, everything on the internet must be true or it wouldn't be on the internet . . . right?

Doug
  • 9
  • 1