I am installing a 60 amp subpanel in a workshop in my backyard and I will have 2 - 20 amp services with 4-5 outlets on each and 1 - 15 amp service for lighting. The length from the main panel to the workshop is about 105 feet. I will be using a double pole 60 and GFI circuit breaker in the main panel to a 60 amp pull out on outside of work shop then inside to the subpanel. What would be a good size wire. I may run one saw at a time or a couple of saws.
  • 20,909
  • 95
  • 135
Harly_Guy
6AWG copper wire would be the minimum for a 60A subpanel but with a 105ft distance you have too much voltage drop and need to go up to 4AWG copper to keep the voltage drop within acceptable limits (usually 5%).
ThreePhaseEel
  • 87,685
  • 144
  • 243
William S.
  • 1,061
The National Electrical Code Book / Article 110.14 (c)(1) identifies temperature limitations for circuits and feeders of 100 amp or less. If the circuit is 100 amp or less you have to size the conductors based on the 60-degree celsius column unless the breaker and the equipment terminations are rated for 75 or 90 degrees.
You have to use a #4 conductor to feed a 60 amp circuit.