I have a concrete slab which can fit a hot tub approximately at a distance of 8 feet from the main breaker panel (located outside on my porch). I assume that I will still need a separate disconnect for the hot tub (minimum of 5 ft from the tub). Can I just pop the disconnect box (with GFCI breaker and 120V outlet) directly next to the main breaker box and then run my #6 cables from there to the hot tub (~20 ft total)? Or does the disconnect need to be separated from the main for some reason? Thanks!
-Phil
Phil B
  • 61
5 Answers5
The pertinent parts of Article 680 I have quoted here:
680.12 Maintenance Disconnecting Means One or more means to simultaneously disconnect all un-grounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be readily accessible and within sight from its equipment and shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool, spa, or hot tub unless separated from the open water by a permanently installed barrier that provides a 1.5 m (5 ft) reach path or greater. This horizontal distance is to be measured from the water’s edge along the shortest path required to reach the disconnect.
680 Part IV. Spas and Hot Tubs 680.40 General Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.
680.40 refers to Part I and the requirement for a disconnect is in Part I (630.12).
This commentary is from the 2011 NEC Handbook:
A readily accessible disconnecting means is required to be located within sight of pool, spa, and hot tub equipment in order to provide service personnel with the ability to safely disconnect power while servicing equipment such as motors, heaters, and control panels. Underwater luminaires are not subject to this requirement. The proximity of the disconnecting means to the pool must be not less than 5 ft unless the disconnecting means is separated from the water by a permanent barrier.
Notice here it says unless the disconnect is separated from the water by a "permanent barrier". If you have a permanent barrier such as a partition between the tub and the disconnect it can be closer than 5 feet. Otherwise 5' is your minimum distance.
So, you were reading the code correctly you need a disconnect in-sight of the spa and mounting next to the main panel will work just fine. Or using a breaker in the panel will work as you and Speedy Petey were discussing.
ArchonOSX
  • 20,870
The disconnect should be mounted outside. One of the main purposes that disconnect panel serves is a lockout/tagout for anyone working on the tub. Other than that, the only other requirement normally was 5 feet from the spa. We normally kept it as close as possible since romex inside the house is normally cheaper than the wiring from the panel to the tub. Also, I've seen inspectors be concerned about the length of flexible conduit (i.e. Carflex), but never had any issue. However, it's always best to ask a real licensed electrician. I only play one on TV.
hopkins-matt
  • 119
You can mount your disconect next to the main. Are you putting your cables in schedule 80PVC? that is what I use in most cases arround pools / spas.
Ed Beal
  • 103,727
  • 79
  • 158
Here in CA the disconnect must also be line-of-sight from the equipment, readily accessible and less than 50 ft from the equipment. Readily accessible means no gates or obstructions between the tub and the disconnect.
bummi
  • 107
Tom Davis
A breaker in the main panel would suffice as the means of disconnect. NO separate enclosure is needed or required.
8' is a prime location since the minimum is 5'. You can just drop a convenience receptacle right from the main panels as well.
Your idea of placing a disconnect panel right next to the main is also fine. It can be as close to the main as you need/want.
Speedy Petey
  • 16,708
  • 54