I've looked at just about every post on adding a C-wire to power a WiFi thermostat but remain uncertain on how to proceed. The current installation on a Rheem RGAC-080A is two wire as here:

XFMR - White -> Thermostat - Red -> Valve TH terminal, Valve TR terminal to silver Honeywell box (capacitor?) -> XFMR

(Tried to take a photo but it's too dark to be informative.)

I can run 3-wire from the thermostat to the furnace and reproduce the Red & White connections. But where does the third wire go? Valve TR?

Thanks.

Edit: Furnace schematic

geoB
  • 211
  • 4
  • 12

1 Answers1

0

Based on your description of the wiring, and the schematic you've provided, this is what I think is going on.

enter image description here
Click for larger view

It sounds like there's a white wire and a black wire, connected to the secondary side of the transformer. The white wire carries 24VAC to the thermostat, which means the black wire is connected to the C terminal.

So the new thermostat should be wired as follows:

  • White -> R
  • Red -> W
  • Extra (blue in diagram) -> C

You can verify this by measuring the voltage between the blue and white wires, in the diagram above. You should get ~24 volts AC, though it might be a bit higher or lower.