33

How much load can a board support, if it is supported only at the ends?

At the moment my specific problem is hanging a tire swing between two trees, and depending on which trees I choose they could be 10, 12, or 14 feet apart (center to center). If I securely attach a 2x4 to the trees and hang the swing from the middle, would it be at risk of breaking from 2 children playing on it (so I'd guess around 300lbs max with them bouncing and jumping onto it)

But my bigger question is the general case: how do you calculate (or where do you look up) what kind of loads can be supported by the wood in question? (other examples would be a 1x10 shelf with supports 24" apart, or 1/2" plywood on a 2' x 4' frame). I'm not an engineer (well, software, but that doesn't count here), but I can do simple math (linear algebra, trig, calculus) and have a basic understanding of physics.

gregmac
  • 29,300
  • 17
  • 89
  • 162
evil otto
  • 513
  • 1
  • 5
  • 10

9 Answers9

24

I'd go with @Aarthi's load bearing table resource for a general idea of what's reasonable.

If you're looking for equations though, you can start with these:

Beam Deflection Formulas

Beam Deflection and Stress Calculator

Area Moments of Inertia

Using the Parallel Axis Theorem

Wood Material Properties (Modulus of Elasticity (E) found in Table 4-3a)

For the dynamic loading, you'll want to do something similar to the fun I had on this question.

...and you may want to consult a good Mechanics of Materials book. (cheaper paperback international edition on Ebay)

As @Ian points out, the problem is not a simple one and is best solved by simply using what's worked for other people in the past. Go take a look at the swings at your local park and use the same size of beam, provided the span is comparable.

Also, if you're really worried, you could always make the rope into a 'Y' to eliminate bending stress on the beam, leaving it solely in shear. This way, the beam is bearing the compression load from the lateral tension on the 'Y', which will keep the trees from bowing toward each other.

Diagram:

|      |______________________|      |
|      |  |                 | |      |
| tree |  |                 | | tree |
|      |__|_________________|_|      |
|      |   \               /  |      |
|      |    \             /   |      |
|      |     \           /    |      |
|      |      \         /     |      |
|      |       \       /      |      |
|      |        \     /       |      |
|      |         \   /        |      |
|      |          \ /         |      |
|      |           Y          |      |
|      |           |          |      |
|      |           |          |      |
|      |           |          |      |
      ...more rope and trees...
|      |           |          |      |
|      |           |          |      |
|      |         -----        |      |
|      |       /  ___  \      |      |
|      |      |  /   \  |     |      |
|      |      |  \___/  |     |      |
|      |       \       /      |      |
|      |         -----        |      |
Doresoom
  • 15,873
  • 32
  • 83
  • 122
13

I'm not a hundred percent sure this answers your question, but I will say this much: 300lbs is actually much, MUCH too low of an estimate, if all of my trolling on this site is anything to go by. Also note that it's not weight but force (ie Newtons) that you need to be looking at.

Second, this document should answer your load-bearing questions. It's kind of technical, though, from what I can tell.

Finally, here is a similar question from DIYChatroom.com.

Wood bears a toleration of roughly 625 pounds per square inch (PSI) of a compression load. Concrete can bear 3,000 PSI of a compression load. Steel can bear 30,000 PSI of a compression load.

Aarthi
  • 1,143
  • 7
  • 20
  • 29
8

Lots of interesting answers for how to figure out the "correct" answer, but hopefully this will help a bit.

We purchased a commercial play set similar to this.

enter image description here

To cover a 12' span, they use three 2x6" beams laminated together - glue, nails and finally carriage bolts.

This is to support 2 swings and a set of rings.

Tester101
  • 133,087
  • 80
  • 327
  • 617
chris
  • 3,291
  • 1
  • 24
  • 20
5

Keep in mind that your load is not static, but dynamic, and the stresses will multiply during the movement of the swing. Also, the movement of the swing will apply stresses against the short dimension of the beam, which it was never intended to support. Looking at the swing sets available at building centers, I've never seen a main support beam smaller than 4 x 6.

Chris Cudmore
  • 14,169
  • 7
  • 61
  • 91
4

This is a fairly complex problem to answer starting from scratch as it has multiple components so I will just summarise the calculations that will need to be done.

In terms of the stresses in the plank, typically as a minimum you will need to calculate the following forces:

  • Bending moments
  • Shear forces
  • Bearing stresses
  • Deflections

These will need to be calculated for different load cases including different locations for the weights on the beam as different positions for the load will give different worst case results. The method of calculation for the stresses will vary depending on the structural details you adopt at the supports but in the case you describe will probably be based on what is known as a simply supported beam.

Having calculated the forces in the beam, you will need to calculate some geometric properties of the beam in order to calculate the stresses. Typical geometric properties will be Second Moment of Area (for bending moments), Shear Area (for shear force), and Bearing Area (for bearing stresses). Again the calculation of these properties will depend on the detailing you choose, as will the use of these properties to calculate the stresses.

The final calculations you will have to do will be the stresses that the wood can withstand. Again, this is somewhat complex because wood, being an organic material, has different strengths in different loading conditions with factors such as grain direction, load type, load duration, wood type, etc. all affecting the calculation. You will also need to include an appropriate factor of safety in the calculations.

Having said all of that, this is over the top for most domestic applications and for the most part basing the size on what has worked in similar circumstances before is normally adequate.

Ian Turner
  • 1,062
  • 3
  • 10
  • 16
3

"...the short answer is, don't use the 2 x 4 for your swing..."

Otis' question was posted long ago, but I thought this may help other people researching similar structural questions. I'm not an engineer, but I've worked with wood for 30+ years.

An interesting question, and one a lot of DIYers ignore, and limit their consideration to one thing: is that 2 x 4 gonna be long enough? The strength, or load-bearing capacity will vary with wood species, and the length of span. A stick of white pine is lighter, but not as strong as yellow pine, plus, you also have to look at the number of knots, and the relative size of the knots because the knots do not add strength, they tend to make break points especially if the knot diameter is more than 1/3 of the face width. The GRADE of your stick is also important, because lower grade, with reduced cross section at the cambium can drastically reduce modulus. The cambium is the ring just inside of the bark. A regular, clear, white pine 2 x 4 stud grade can support static load of about 450 pounds for a 4' span and about half that for the 8' span with the lowest fiber stress capacity of 900psi. per the safe load table in WSDD So, the short answer is, don't use the 2 x 4 for your swing, and I think a 2 x 12 would be your least 2x for the span you're considering. This says nothing about the shear forces at the attachment points, but suffice to say that 16d nails won't be enough- put 3, 3/8"x 6" lags w/washers - MINIMUM. The first rule of DIY is, Safety First; Design in strength to design for safety.

David
  • 31
  • 1
2

There is an online calculator called the Sagulator that estimates the deflection in a shelf given its dimensions, the type of wood, and the load.

matsukaze
  • 251
  • 1
  • 1
1

Don't use a 2x4 for a 10' span. It will barely support itself without sagging. If it sags it's not strong enough. Your second problem is going to be not just that it won't support a big dog but that as they swing the board has the tendency to bow, which weakens its ability to support even more.

Use two 2x12s. Use 2x4 spacers between the 2x12s every 16". Don't nail them, use 3" exterior screws, 4 on each side. If the swinging still causes too much movement another board can be placed on the top our bottom to stop movement.

isherwood
  • 158,133
  • 9
  • 190
  • 463
1

An alternative option nobody seems to have mentioned is to use a tubular (round or square) galvanized steel fence post between the trees. You could attach it to each tree by lashing it in place with rope.

Craig Tullis
  • 6,034
  • 1
  • 19
  • 29