3

We're selling our home and the buyer's inspector says the white cable in these photos must be protected from damage, by either a conduit or instead using a metallic cable. It's connected to the furnace, which is in our attic (no stairs/ladder access -- a ceiling hatch 6.5 feet away, instead).

The furnace installer, the electrician, and another home inspector all say it doesn't need protection. If these folks are right it could save me an expensive electrician visit that it sounds like I don't really need!

I would love it if somebody could cite the code for me so I can give the inspector more than just a bunch of opinions.

Thanks, - Rich in Woodinville Top of furnace; note white NM cable

Cable goes behind the furnace and down through floor.

2 Answers2

4

They are apparently considering the attic accessible although it is not readily accessible. Most furnaces in basements have NM cable protected with EMT conduit and that is probably where they are equating that situation to this one. However, in a normal basement the cable would be readily accessible, meaning you can walk right up to it without any tools or ladders.

So, it doesn't need protection since it is not readily accessible being that it is in an attic that needs a ladder for access. However, it does need to be secured and supported according to the code. Meaning within 12" of of the switch box in your picture and every 4 1/2 feet thereafter.

From the 2014 National Electrical Code:

334.30 Securing and Supporting.

Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (41⁄2 ft) and within 300 mm (12 in.) of every outlet box, junction box, cabinet, or fitting. Flat cables shall not be stapled on edge.

It is up to the HVAC technician and electrician to agree on a method and location of securing it to the AC cabinet.

Good luck!

ArchonOSX
  • 20,870
  • 3
  • 30
  • 53
3

This answer has some of the applicable codes for protecting NM cable in an attic. Since there's no stairs or permanent ladder, and the cable is more than 6' from the entrance of the attic. Protection is not required in this situation.

If the inspector tries to call you out on not securing the cable within 12" of the switch box, simply have them read 334.30(B).

334.30(B) Unsupported Cables Nonmetallic-sheathed cable shall be permitted to be unsupported where the cable:

(2) Is not more than 1.4 m (4 1/2 ft) from the last point of cable support to the point of connection to a luminaire or other piece of electrical equipment and the cable and point of connection are within an accessible ceiling.

Tester101
  • 133,087
  • 80
  • 327