I have a standard British heating configuration at home - there is one gas heater that provides hot water both for the boiler (and bathroom etc.) as well as for central heating. There is a small electronic device where you can set if you want to heat the water or run the central heating (it has a timer, etc). The central heating works based on a thermostat in the living room, which shows green when the actual temperature is lower that the set value (hence the heating is working), or red otherwise.
Recently we switched the central heating on for the first time this year, but it didn't work as expected. When the hot water is off everything seems fine. But when the system heats the water up, all the radiators got boiling hot, despite the thermostat showing red all the time. What might have gone wrong? Is it something I could fix myself?
EDIT: To be more precise I did a test and the results are as follows:(CH - central heating, HW - how water)
  • HW off, CH off - everything cold [OK]
  • HW on, CH off - everything is hot [WRONG]
  • HW off, CH on, temp > thermostat - everything cold [OK]
  • HW off, CH on, temp < thermostat - everything cold [WRONG]
  • HW on, CH on, temp > thermostat - everything hot [WRONG]
  • HW on, CH on, temp < thermostat - everything hot [OK]
So it seems that the hot water switch now operates both HW and CH, and the central heating switch does nothing at all (and thermostat is likewise ignored). Is this something I could fix myself?
ChrisF
  • 16,973
  • 74
Grzenio
  • 225
A lot depends on the type of system you have. If you have a system or combi boiler, it could be the diverter valve which is faulty. This will be in the boiler itself. If you have a Y-Plan system with a three port valve, it could be the three port valve which is faulty. These are usually found in your airing cupboard or in your loft.
Tom Pickles
  • 186
One of two immediate problems come to mind.
1) Bad thermostat, causing the heating system to move water through the system constantly despite the current temperature
2) Failed circuit in the boiler system itself, causing it to THINK the thermostat is calling for heat.
A quick test would be to remove the thermostat from its mounting (usually they just snap in place) and see if the heat shuts off. If that works, replacing the thermostat is a fairly easy process if you follow the directions carefully and make sure you tag all the wires properly.
Otherwise you'll need a pro to come check your system.
The Evil Greebo
  • 25,971
  • 91
  • 125