At our studio we have a NEMA 14-30R outlet used for our kiln. When not in use, we want to use another piece of equipment that has an L6-30P plug. I believe the equipment is rated at 8AMP 240V.

I built an adapter that has a 14-30P on one end and an L6-30R on the other, capping the neutral inside the L6-30R. In this way we can switch from one piece of equipment to the other without running a new line, guaranteeing mutually exclusive use of the circuit.

Is this configuration safe? Would I be better off pulling off the neutral pin from the 14-30P? Right now I just want to make sure no one is going to hurt themselves until we can find an appropriate solution although running a new circuit is not an option - maybe sub-panel with a switch between two outlets?

ThreePhaseEel
  • 87,685
  • 36
  • 144
  • 243
Steven
  • 551
  • 1
  • 10
  • 23

1 Answers1

4

Your adapter is probably safe. However, I would have used a 3 conductor cable instead of a 4 conductor cable; that way there is no neutral to cap.

Another option would be to cut the plug off the end of the other piece of equipment and wire on the 14-30P.

A third option would be to wire up an 14-30 receptacle right next to the existing L6-30 receptacle, using the same circuit. As long as you are using only the kiln or the other equipment and not both at the same time, that's fine. If you really wanted to prevent both from operating at the same time, you could get a transfer switch, but that's probably overkill.