I live in a (rented, 1980 built) row townhouse in the USA with slightly suspect electricity:
  • A few of the outlets and light switches in the house (in various rooms) don't work at all. (Even allowing for some switched outlets.)
  • My five year old desktop computer on the ground floor developed a bad power supply a few months after moving in. (After a cross-country trip in a moving van, and it is an old computer.)
  • Plugging anything into one outlet on the ground floor often shorts out the rest of the stuff in the room. (We avoid using this outlet!)
  • A 5-6 year old laptop's power adapter doesn't work on the ground floor, but does work upstairs. (A newer laptop works both upstairs and downstairs, so it's possibly a bad power supply on the old laptop.)
Given that the computers in question are 5-6 years old, and we jostled them across the country moving, it's entirely possible that their time had/has come and they need to be replaced. However, before I buy and plug in a new desktop (or keep using my other newish computer) with this potentially suspect power, am I right to be concerned about it? Could the damage have been caused by the times we've shorted out the downstairs room? Or maybe slowly over time by bad power?
If I had a multimeter or some other test device, could I test my outlets and/or electricity? Do I need to call an electrician? Should I just assume that my computer died of old age and replace it without worrying that the new one will meet a similar fate?
Mike Kale
  • 143
Yikes, it sure sounds like you have several issues with your electical wiring there. I won't speak too much to your power supply issue, but really think you should invest in a UPS to mitigate any power related damages to your equipment.
Now lets correct a few mistakes in the previous answer.
The 120VAC legs of your electrical service are supplied by two separate hot feeds from the power company. The neutral is not there to split the 220VAC, but rather to supply a return path to the service panel and ultimately earth ground.
The neutral should be at the same potential as ground. An open neutral is checked by measuring neutral to ground, if line voltage appears, then in fact the neutral path to ground is open. Unless you have a situation where both 120VAC legs are in contact with one hot connection, you cannot produce more than 120VAC on any open neutral. If you were to see 140VAC on any hot to ground or neutral, or neutral to ground, then you have some serious problems and time to call the landlord before you fry all your lights, appliances, and electronics. This situation is very rare, and I don't think it is your problem. Your problem sounds more like a bad connection, either hot or neutral in some device that feeds your downstairs outlets.
This can be a frustrating and time consuming job to track down this type of problem. It may involve pulling several devices out of the boxes and testing voltages with the power on, and also testing conductivity with the POWER OFF. Unless you have the experience and you feel very comfortable working on hot wiring, I'd suggest you have the landlord call in an electrician ASAP.
Jay Bazuzi
  • 11,778
  • 100
  • 143
shirlock homes
  • 58,628
  • 87
  • 168
The worst electricity fault that a house or apartment can have is an open neutral. The neutral is the wire that splits the 220V coming into the house into two different 110V feeds. If the neutral is open, there is nothing keeping them both at 110V. For example you could turn a light on, and the side with the light could drop to 80V, and the other would go up to 140V.
Some of the outlets in your apartment are tied to one side, the rest are tied to the other.
You can check for an open neutral by turning lights on and off throughout the apartment. If turning on a light in one room makes the light brighter in another, you have an open neutral. You shouldn't use your computer, in fact you should get it fixed immediately, it's quite dangerous.
Other possible faults include swapped wires on the outlet, open ground, open hot. These can all be checked with a $5 outlet tester that you buy at Home Depot.
The electricity problems you describe are absolutely intolerable and I would request the landlord repair them immediately. You can't do your own work on a rented unit because a licensed electrician must do all work in a rental unit.
This certainly sounds bad enough that it's not legal for it to continue in service. If the landlord is not responsive, a talk with the local city electrical inspector may compel a repair, at the risk of having to move (because it may not be feasible to do repairs while the unit is occupied.) That property manager may also not want to work with you at that point.
As far as dirty power, usually your worst enemy is the other stuff in your own home. We have a small building where it's obvious the guy was on full defence against power problems, with every power conditioner known to man installed. The building had a dedicated transformer. And also a bunch of ratty old fluorescent ballasts. Gee. Got some nice GE ballasts with 99%PF, solved.